Thanks Bill.
 
I would like to sit in on TC meetings, in the corner perhaps, napping on and
off, and I would feel qualified enough to be the person who went out for
coffee and sandwiches in the wee hours of the debate. It takes me too long
to figure things out though to catch anything early in the process.
This issue is different-- 14 years ago Tom's results were not accepted
because there was not enough data, tests, calculations, etc., to back them
up. Now his results ARE accepted-- why? Is it because they are backed-up
now? No. It is because 1" max gap width per foot of ceiling height has been
shown to be conservative in itself, so the only hammer SOMBODY had left was
to 'virtually limit the ceiling height'. Ridiculous.

Thanks again Mr. Brooks,

Brad

-----Original Message-----
From: Bill Brooks [mailto:[email protected]] 
Sent: Friday, September 19, 2014 9:10 AM
To: [email protected]
Subject: RE: Cloud Ceiling Article in Sprinkler Age (Get Involved)

Brad, you need to 1) start submitting proposals and comments during the NFPA
Standards cycle, and/or 2) apply for a seat on one of the Technical
Committees.  It is an awakening process to see the way a typical committee
operates.  In my experience there is a handful of opinion leaders on each
committee who drive the process forward.  It's best to figure out who these
individuals are and attempt to understand their motivations.  The process is
set up to make it difficult to overturn committee actions.  This is good or
bad depending on your point of view.  All this said, it is actually possible
to affect a change if you are persistent.

The NFPA website has all the proposals and comments for each Standard, along
with the committee action.

Bill Brooks

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Friday, September 19, 2014 9:39 AM
To: [email protected]
Subject: Cloud Ceiling Article in Sprinkler Age

Good Article by Tom Wellen in current Sprinkler Age.

Tom did the original modeling in 2000, and came up with max gap width 8" (to
not need heads above).

The recent tests and modeling confirmed that, but showed it was reasonable
to extend it to allow 1" gap width per foot of ceiling height, so at 12'-0"
ceiling height the gap between clouds could be 12" and not need heads above.

There are other rules that apply. 

I found it disturbing that the TC decided to "go conservative" after all
that and say 8" max gap width PERIOD. That really gives the Architects a lot
of leeway in the design phase... (frigging) NOT!

Design by Committee. That is something to NITMAM if I ever did see one, and
I will if I get a chance. 

 

Is there somewhere I can see whom voted for what on this issue, a link or
something? I've been stewing over this for a few days now, and it doesn't
help to 'talk it out'.

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to