Regardless of if you're 9 ft off a wall your overall coverage still cannot
exceed the values in 8.6.2.2.1(a).

On Fri, Sep 26, 2014 at 10:20 AM, Parsley Consulting <
[email protected]> wrote:

> Jerry,
>     I don't know what anyone else is going to use to answer this, however
> I've always regarded the answer as "yes".  Here's why - by definition a
> small room does not exceed 800 square feet, per 3.3.21.  Let's say for
> argument that the room you're looking at is 800 square feet.  You would
> need at least two sprinklers, since the maximum coverage for any single
> sprinkler cannot exceed 400 square feet, per 8.5.2.2.2.  It's still a small
> room, if light hazard, and those rules 8.6.3.2.4.1 still apply.  NFPA 13
> points to allowing more than one sprinkler in a small room in 8.6.2.1.2.1,
> as it suggests that the coverage area per sprinkler is based on the square
> footage of the room divided by the number of sprinklers (plural) in the
> room.
>
>     Seems to me you can.
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/> ***
>
> On 9/26/2014 8:48 AM, Jerry Van Kolken wrote:
>
>> I've been reading this thread and come to think I've miss understood how
>> to
>> apply this exception.
>>
>>
>> Based on NFPA 13(13ed)Fig A.8.6.3.2.4 I've always thought the only time
>> you
>> would exceed the 15'-0" spacing for a sprinkler is when you have a single
>> sprinkler in a small room.
>>
>>
>> In a situation where an L shape room 12x18 with a 4' pop out for the entry
>> in one of the corners along the 18' side, Could you get away with 2
>> sprinklers or do you need 3?
>>
>>
>> Jerry Van Kolken
>>
>> Millennium Fire Protection Corp.
>>
>> 101 Copperwood Way, Suite H
>>
>> Oceanside, CA 92058
>>
>> (760) 722-2722 FX 722-2730
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>>
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to