I see some worms peeking through the lid of the can.  Is this going to
spiral us down the EOR hole again or is this another hole occupied by
sprinkler designers/contractors?

Bill Brooks

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Monday, October 06, 2014 10:34 AM
To: [email protected]
Subject: RE: Shadowed area behind built in cabinet and in widow sill

1.7 New Technology "Nothing in this standard shall be intended to restrict
new technologies or alternate arrangements"... Based on the recently
discussed conservative committee actions I would think that anything in the
later editions of 13 should be allowed as an "alternate arrangement".  Say
something in 2002 edition that was later proved to be wrong through full
scale testing. Would you force a licensed contractor to install it wrong
because the AHJ hasn't adopted the standard with the new data with the
corrections? Or as a licensed contractor would you knowingly install
something that has been proven to be wrong by today's standards because it
was okay in the 2002 editionRon F 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Monday, October 06, 2014 6:50 AM
To: [email protected]
Subject: RE: Shadowed area behind built in cabinet and in widow sill

There are two lines of reasoning I have seen on matters such as this:
1."We aren't following the newer NFPA 13 - period."
2."The newer standard may have what the NFPA committee believes to be the
best criteria, but the ICC and our local codes folks have not weighed in on
the changes to the standard. Therefore, we cannot accept those
'clarifications.'

WE may KNOW that the changes won't affect the future code revisions; but the
AHJ doesn't know and most times won't take the chance.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Friday, October 03, 2014 7:02 PM
To: [email protected]
Subject: Shadowed area behind built in cabinet and in widow sill

We are bound to NFPA 13 (2002).  We have an ECHSW above the door in a room.
On the opposite wall is a window and sill that does not create an additional
floor area.  There is a built in cabinet that partially obstructs the window
sill and creates a shadow of 2 sq.ft. between the cabinet and the window
over the window sill.  We informed the AHJ that per NFPA 13 (2007) 8.5.3.2.4
sprinklers are spaced to walls and not windows if they do not create
additional floor area.  We also pointed to NFPA 13 (2013) 8.1.1(3) &
A.8.1.1(3) which indicate shadow areas are acceptable so long as the other
obstruction guidelines are followed.  The AHJ stated they cannot accept the
newer standard clarifications on this issue.

Is there something I am missing in NFPA 13 (2002) that states this design is
acceptable?

                                          Thanks,

Sean




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to