I would have thought unstable due to "spillage of contents. The frames around 
the totes are not fully enclosing them. Therefore; the contents could flow 
freely once the plastic melts.
I could be just reading it too deeply. First cup is underway...


R/
Matt

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larry Keeping
Sent: Friday, October 31, 2014 8:46 PM
To: [email protected]
Subject: RE: Plastic classification

Regarding your original question though, I think you answered your own 
question. If the framework around the totes keep them from collapsing, the 
piles are stable.

3.9.2.4*   Pile Stability, Stable Piles.   Those arrays where collapse, 
spillage of content, or leaning of stacks across flue spaces is not likely to 
occur soon after initial fire development.

3.9.2.5*   Pile Stability, Unstable Piles.   Those arrays where collapse, 
spillage of contents, or leaning of stacks across flue spaces occurs soon after 
initial fire development.

Larry Keeping, P.Eng.

Professional Loss Control
3413 Wolfedale Road, Suite 6
Mississauga, Ontario
L5C 1V8

Phone:   905-949-2755, ext. 204
Fax:        905-949-1752

E-mail:    [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott A Futrell
Sent: October-31-14 12:37 PM
To: [email protected]
Subject: RE: Plastic classification

Jay,

Totes that "...are being cleaned of any solution that may have been in them..." 
are considered FULL by definition in the International Fire Code (IFC).  So, IF 
the IFC is enforceable your client may have a different problem on their hands 
that they are not aware of, and don't want to hear about.

The first question needs to be, what was in the totes and then how should they 
be protected.  IF it is non-toxic, non-hazardous, and not flammable or 
combustible liquids, then you are back to your original question.

Good luck.

Scott Futrell
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jay Stough
Sent: Friday, October 31, 2014 11:20 AM
To: Sprinkler Forum
Subject: Plastic classification

I am looking at a warehouse that has 100 to 300 gallon plastic totes that are 
supported by a rack around each tote.  This allows the totes to be stacked 3 
high, for a height of approximately 16'.  These totes are empty and in the 
process of being cleaned of any solution that may have been in them so they can 
be used by other customers.  As I look in NFPA 13 (2007) at the definition of 
stable and unstable piles, it appears that these would be stable piles, 
requiring more water than unstable piles.  If there is a fire in a lower tote, 
I am sure the fire might extend to a tote above, but due to the steel racks, 
they would not fall over.  However, due to the openness of the racks, the water 
would be able to get to the bottom of the pile quickly, hence limiting it to 
the pile that is on fire.
Would you classify these as stable piles?  The difference is a .4/2500 for 
unstable versus .7/2500 for stable.

--
*Jay Stough*
NICET IV LAYOUT
NICET III ITM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to