Generally, very generally speaking,  if the floor is involved and
contributing significantly to a fire, there are real problems.    That does
not mean, by most means, that floors do contribute significantly to
fires.   Floors usually do not contribute significantly to fires, even with
combustible material.

Years back (15 years), I remember NFPA 101 was considering relaxing their
flame spread rating on flooring in exits, because floor material is usually
so inconsequential, to a fast growing fire.​  NPFA 101 may well have
relaxed their requirements;  I didn't follow up on the results.  There was
reason for this consideration on relaxing the prescriptive performance of
flooring.  By the time the floor became significantly involved, the fire
has usually already defeated whatever suppression system was supposed to
control it.  By the time flooring significantly contributes to most
non-arson fires, the other combustibles are already well off and their
pyrolysis is pushing the fire in the direction of flashover.

Flashover is not a real risky proposition on a very large open space such
as a soccer/football pitch with few combustibles at elevated levels above
the floor.

My overall consideration of this seemingly hazardous situation, is that it
is not as hazardous as your fears imagine it to be.   Sure, if someone
comes in and pours gasoline on a large area of the ground up tire inlay,
there could be a large initial fire.   But if you believe at full occupant
load that evacuation can reasonably occur in 4 minutes (or well before a
hazardous layer envelopes building occupants), then I would sleep sound at
night with the 0.2/1,500 sprinkler system you have described for this
situaiton.

Yes, this decision is accepting a risk.  The Dutch accept (and have the
courage to publish the acceptance) of killing ~1,500 people by sea levee
failure, with the likelihood estimated in the 1 in 40,000 range.  Short of
a arson situation, I think the risk of death by fire-in-tiny-spheres of
ground-tire to be significantly less than this risk accepted by the Dutch,
both in terms of likelihood of occurrence and in terms of final death
count.    The Dutch are, in my opinion, world-class leaders in risk
acceptance and likelihood estimation.

If you are looking for some peace-of-mind, ask for two samples of the
flooring.   Burn the samples in a worse-case scenario (corner
configuration).  You will have trouble igniting the rubber spheres.
Sprinkle gingerly with gasoline and attempt re-ignition.  Remember though
that small scale tests do NOT duplicate real-scale fires.  Small-scale
fires often underestimate the fire growth rate and size.

My apologies for a brusque treatment of a sensitive subject (fire deaths),
but this is where the rubber meets the road.


Scot Deal
Excelsior Risk/Fire Engineering
gsm:  +33 (0) 64.96.67.44.46



Chris Ellsworth
Sent: Friday, November 21, 2014 10:03 AM
Subject: Indoor Soccer Facility

We were contracted to do a few add/relocates on an existing concrete tee
construction facility.  A flag was thrown up once we found out what was
being installed for this tenants flooring.  They are using an astro turf
type field.  The problem isn't with the turf itself.  It has undergone
extensive testing to prove that it is not flammable.  The problem is with
the inlay.  They have used the type of inlay you would see on an outdoor
facility which is ground up tires.  I have checked with the plant manager
who supplied their product and they do not use any type of a fire proofing
spray on the product.  Essentially it is ground up tires.  We have a deck
height of approximately 16 feet and it is double tee concrete construction.
The fire marshal and my concern is that the existing sprinkler system can
not handle this type of fire.  I have already calced it and the best the
system could do is a .2/1500.  This gives a 13 lb safety.  Has anybody
dealt with anything close to this on an indoor facility and should we be
concerned with this inlay?  Thanks in advance.







_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



-- 
Amo a los que puede sonreír a sus problemas, que puede tomar fuerzas de sus
angustias, y crecer valiente entre reflejo. Es el negocio de las mentes
pequeñas a disminuir, pero cuyo corazón está firme, y cuya conciencia
aprueba su conducta, continuarán sus principios hasta la muerte  - da vinci

Scot Deal
MSc Fire Protection Engineer/BSc Chemical Engineering
Chartered Engineer EU Schengen
Chartered Chemical Engineer, Engineers Australia
Licensed Fire Protection Engineer, Oman
FPE/PE USA