An account has had the wet sprinkler system changed to antifreeze. Too bad the 
alarm guy did not know about the antifreeze.  Maybe there is a reason for 
signs.  When I checked the antifreeze solution at the far end, it was at 10°F. 
We will install an isolation valve so the system can be flow tested w/o loosing 
the antifreeze solution, and install a test port at the far end.  The system is 
about 50 gallons, so we do not need to test the antifreeze except at both ends. 
 

And isn’t the expansion tank  supposed to be listed?  The tank does not have 
any ID as to manufacturer or listing or capacity.  Other tanks I have seen were 
mounted vertically, this one is horizontal. 

There are at least 2 places where the wet sprinkler piping goes vertically 
about 15 feet.  Do we need to loosen the sprinkler heads to allow air to escape?

We now get our antifreeze pre-mixed in 5 gallon buckets.  Any leftover 
antifreeze will be left on site. And signs will be installed.  One sign we make 
by cutting an empty bucket so the label becomes the sign.  

What did I miss?  