As strange and contrary as it sounds, a single interlock preaction system with 
less than 20 heads may not need any air or nitrogen source. So it then wouldn't 
need the low air switch either.

Is this really correct?

7.3.2.1 describes the 3 types of preaction systems
(1) Single interlock
(2) Non-interlock
(3) Double interlock

Then 7.3.2.4 Supervision 
The annex describes supervision as constant monitoring of pipe and detection 
equipment to ensure the integrity of the system. It then explains that a single 
interlock system of more than 20 heads is required to be supervised but not at 
a minimum pressure.
The handbook also describes why a minimum pressure of 7 psi is required on 
non-interlock and double interlock but doesn't mention single interlock.

7.3.2.4.4 states; All precation system types described in 7.3.2.1 (2) 
non-interlock & (3) double interlock shall maintain a minimum supervising air 
or nitrogen pressure of 7 psi.

It does not mention Single interlock.


If you do decide to install a compressor or nitrogen source, it needs to be an 
automatic source of air or nitrogen with an AMD. You can't just rely on "Joe 
the maintenance guy" to turn on the compressor occasionally. What if Joe goes 
on vacation or gets hit by a bus?
Also, you don't have a low air supervisory switch ring a bell. A bell is 
associated with alarm; fire, get out of the building. Low air is just a 
supervisory condition, that's when you call Joe the maintenance guy. Then you 
find out Joe got hit by a bus...

Kind regards,

mike

Mike Henke CET
Sprinkler Product Manager
___________________________________________________

Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936 | direct: 314-595-6740
[email protected] | www.pottersignal.com








-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Charles Thurston
Sent: Wednesday, December 17, 2014 6:19 AM
To: Colin Carew (Cambridge)
Subject: Re: single interlock pre-action less than 20 heads

Hello Colin,

I'm no expert, But reading 7.3.2.4.1 the word "automatically" triggered in my 
mind that if there is less than 20 heads, You still need the compressor. Just 
don't need the pressure switch to turn the compressor on/off, Maint guy could 
go by and cycle it daily or as needed. Would still need the low air switch but 
it is allowed to just ring a bell on the wall.

Tuesday, December 16, 2014, 12:43:48 PM, you wrote:

> 7.3.2.4.1

> Sprinkler piping and fire detection devices shall be automatically 
> supervised where more than 20 sprinklers are on the system .


> Would I be correct  I do not require an air compressor  in turn no low 
> switch either ?  I just want to make sure I am reading it correctly . 
> I have done this in the past , I am just Second guessing myself .

> Thanks .

> Colin Carew







> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org



--
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to