Bleeping spellcheck. It turned QR into WA.

SL





<div>-------- Original message --------</div><div>From: Steve Leyton 
<[email protected]> </div><div>Date:12/22/2014  6:35 PM  (GMT-08:00) 
</div><div>To: [email protected] </div><div>Subject: RE: 
Do normal yearly fire sprinkler inspections review forolderheads? </div><div>
</div>Fast Response is a parent category that includes WA and Residential 
sprinklers.

Steve L. 





<div>-------- Original message --------</div><div>From: 
"[email protected]" <[email protected]> 
</div><div>Date:12/22/2014  5:48 PM  (GMT-08:00) </div><div>To: 
[email protected] </div><div>Subject: Re: Do normal yearly 
fire sprinkler inspections review for   olderheads? </div><div>
</div>So a QR head is fast response? I was under the impression they were 
different RTI's

Jeff
JB Fire Protection
Sent from my iPhone

> On Dec 22, 2014, at 16:46, Duane Johnson <[email protected]> wrote:
> 
> QR has an FR element. But FR can also equal RES. FR can also equal extended 
> coverage standard response or even ESFR. In other words there are many 
> sprinkler types that have fast response elements. 
> 
> Duane Johnson 
> Strickland Fire Protection
> Sent from my iPhone
> 
>> On Dec 22, 2014, at 6:18 PM, Jeff Bridges <[email protected]> wrote:
>> 
>> One additional question also-
>> IS it QR or FR heads that need to be tested at 20 years/ every 10 thereafter?
>> Section 5.1.1.1.3 says fast response elements.
>> Maybe I'm missing something?
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Roland Huggins
>> Sent: Monday, December 22, 2014 7:55 AM
>> To: [email protected]
>> Subject: Re: Do normal yearly fire sprinkler inspections review for older 
>> heads?
>> 
>> It’s NOT part of the annual or the 5 yr.  IT is part of the 20 yr for QR and 
>> 50 yr for SR.  Technically there is no such thing as an annual inspection 
>> per NFPA 25.  There are items with an annual frequency but it’s not uncommon 
>> to check all items with a frequency up to 1 yr during that inspection.   
>> Having said that, we had it as part of our old 5 year form just to ensure it 
>> was recorded somewhere.  It gets an N/A util the system is older.
>> 
>> Roland
>> 
>> 
>> Roland Huggins, PE - VP Engineering
>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
>> Dallas, TX
>> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>> 
>> 
>> 
>> 
>> 
>>> On Dec 20, 2014, at 4:02 PM, Jody Massey <[email protected]> 
>>> wrote:
>>> 
>>> I know that this is probably a stupid question...
>>> 
>>> I know that NFPA requires the following, but is it part of the annual 
>>> or 5 year inspection? In other words, do I need to review this myself 
>>> separately.
>>> 
>>> Per NFPA-25, 2011, section 5.3.1.1.1 if sprinklers are 50 years old 
>>> they shall be replaced or have a representative sample tested. They 
>>> must be tested every 10 years after that.
>>> 5.3.1.1.2 states if the sprinklers were manufactured prior to 1920 
>>> they shall be replaced.
>>> 5.3.1.1.1.3 states if they are quick response heads, after 20 years 
>>> they must be replaced or have a sample tested.
>>> 
>>> I just need to be sure. Thank you or your insight.
>>> ᐧ
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to