Consider NFPA 13 (2013) as the applicable standard.

Question - Why are check valves required on each sprinklers system riser when 
buildings are over 2 stories in height but they are not required on each system 
riser when the building is single story (ex: warehouse with multiple systems on 
a manifold)?

Please assume for this question each system will have a DCBFP device between 
the city water connection and the building.  Also please assume the FDC (with 
check valve) is tied directly into the manifold/standpipe downstream of the 
DCBFP and prior to any system control valves.

My code references are as follows:
3.5.12 System Riser - The aboveground horizontal or vertical pipe between the 
water supply and the mains (cross or feed) that contains a control valve 
(either directly or within its supply pipe), pressure gauge, drain, and water 
flow alarm device.
8.16.1.5.1 - Multistory buildings exceeding two stories in height shall be 
provided with a floor control valve, check valve, main drain valve, and flow 
switch for isolation, control, and annunciation of water flow on each floor 
level.
8.17.5.2.2(1) - Each connection from a standpipe that is part of a combined 
system to a sprinkler system shall have an individual control valve and check 
valve of the same size as the connection. [This is identical to NFPA 14 (2013) 
- 6.3.5.1]

What I do not understand is why check valves would be required on each system 
riser when you go vertical, but not horizontal.  Any clarity on this question, 
specifically "WHY" would be greatly appreciated.

Thanks,
Sean


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to