As a fitter it is helpful when check valves are added to multi story to avoid closing every control valve on every floor. Not for draining but rather for filling. When filling any particular floor pressure can bleed off other floors then setting off flow switches when it re- pressurise.
Sent from my Verizon Wireless 4G LTE smartphone <div>-------- Original message --------</div><div>From: "Morey, Mike" <[email protected]> </div><div>Date:01/21/2015 6:40 PM (GMT-07:00) </div><div>To: [email protected] </div><div>Subject: Re: Why are check valves required on each system in buildings over 2 stories but not in multisystem 1 story buildings </div><div> </div> I believe the handbook explanatory material for at least one of those sections points out that it requires the check valves on multistory buildings to prevent the need to shutdown every floor individually to expedite draining, which adds an additional failure point (control valve left shut). > On Jan 21, 2015, at 11:42 AM, [email protected] wrote: > > Consider NFPA 13 (2013) as the applicable standard. > > Question - Why are check valves required on each sprinklers system riser when > buildings are over 2 stories in height but they are not required on each > system riser when the building is single story (ex: warehouse with multiple > systems on a manifold)? > > Please assume for this question each system will have a DCBFP device between > the city water connection and the building. Also please assume the FDC (with > check valve) is tied directly into the manifold/standpipe downstream of the > DCBFP and prior to any system control valves. > > My code references are as follows: > 3.5.12 System Riser - The aboveground horizontal or vertical pipe between the > water supply and the mains (cross or feed) that contains a control valve > (either directly or within its supply pipe), pressure gauge, drain, and water > flow alarm device. > 8.16.1.5.1 - Multistory buildings exceeding two stories in height shall be > provided with a floor control valve, check valve, main drain valve, and flow > switch for isolation, control, and annunciation of water flow on each floor > level. > 8.17.5.2.2(1) - Each connection from a standpipe that is part of a combined > system to a sprinkler system shall have an individual control valve and check > valve of the same size as the connection. [This is identical to NFPA 14 > (2013) - 6.3.5.1] > > What I do not understand is why check valves would be required on each system > riser when you go vertical, but not horizontal. Any clarity on this > question, specifically "WHY" would be greatly appreciated. > > Thanks, > Sean > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org