Reference NFPA #30 2008 ed.

 

We have class 1B & 1C in 45 gal metal drums non-relieving, stored on single
row racks to 20'

 

Table 16-5.2.1

 

Ceiling density of 0.40 over 3000 sq.ft plus in-racks following layout "E"

 

Section 16-5.1.10(5) layout E shall mean one line of in-rack sprinklers in
the flue space at every storage level above the floor and face sprinklers at
the first storage level at each rack upright. In-racks sprinklers shall be
spaced not more than 9 ft on center and staggered vertically. 

 

My question is if I have single row racks I have no flue space, so I would
run the piping in the rack, but do I still need the face sprinklers?

 

I have never done face sprinklers on single row racks.

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.