Reference NFPA #30 2008 ed.
We have class 1B & 1C in 45 gal metal drums non-relieving, stored on single row racks to 20' Table 16-5.2.1 Ceiling density of 0.40 over 3000 sq.ft plus in-racks following layout "E" Section 16-5.1.10(5) layout E shall mean one line of in-rack sprinklers in the flue space at every storage level above the floor and face sprinklers at the first storage level at each rack upright. In-racks sprinklers shall be spaced not more than 9 ft on center and staggered vertically. My question is if I have single row racks I have no flue space, so I would run the piping in the rack, but do I still need the face sprinklers? I have never done face sprinklers on single row racks. Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org