Commentary from the 2012 handbook:
All required or provided life safety or fire protection related
equipment must be continued in use and be maintained to meet the
requirements in effect at the
time of the original installation. Non-required equipment that has been
taken out of service or cannot function as intended must be dismantled
and removed to prevent creating a false impression of protection. Simply
because a non-required system does not meet the current standards is
neither cause to require its removal (see Section 901.4), nor a reason
to require the system to be upgraded. As long as the system is
maintained in the manner in which it was intended when installed, it can
be allowed to continue.
Interesting stuff.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 1/28/2015 4:41 PM, Travis Mack wrote:
*901.4.5 Appearance of Equipment*. Any device that has the physical
appearance of life safety or fire protection equipment but that does
not perform that life safety or fire protection function shall be
prohibited.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 1/28/2015 5:37 PM, Cahill, Christopher wrote:
IFC early part of Chapter 9 I believe. I don't have it handy to give
you the exact section.
Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone: 952.656.3652
Fax: 952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN
Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For
-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Thomas Watt
Sent: Wednesday, January 28, 2015 5:46 PM
To: [email protected]
Subject: Sprinkler cameras
I know these are prohibited by code/standard but cannot find the
section to prove it.
Little help please???
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org