Looking for a 'like' button here, but your response demands a standing ovation, 
Jerry.

I too have had many conversations with AHJ's in this manner.  Unfortunately, in 
the arena I work in, the AHJ's write their own code superseding NFPA.  

13d is about life safety for an incident involving the occupants of the house, 
let's leave it that way so it can continue to have a chance to be affordable.  


Tim Roach
Hyperion Fire Protection
3196 Wild Horse Court
Thousand Oaks,  CA 91360
[email protected] 
805 427-4299

<div>-------- Original message --------</div><div>From: [email protected] 
</div><div>Date:01/30/2015  7:11 AM  (GMT-08:00) </div><div>To: 
[email protected] </div><div>Subject: Re: 13D exterior 
overhangs COMMENT </div><div>
</div>Ladies/Gentlemen:

Regarding the overhang, I have a not dissimilar situation with  a new 13'D' 
residence/single-family/two-story dwelling. The AHJ/plans reviewer  spotted 
an elevator in the house. She wanted to see detail of shaft construction  
(combustible materials) - she states a sprinkler is needed in the shaft. No,  
says I - 13'd' specifically states not required. After consulting with  her 
supervisor (Fire Marshal), they relented, however, it was "going in the  
file" that the AHJ urged us (me) to provide the sprinkler in the shaft.  
Okay...Could I have deferred and simply gone ahead and added ONE sprinkler? Of  
course. But I made the decision after not only reviewing the Code, but 
searching  the fire "area of origin" in the back of 13'D'. Granted, few homes 
have 
elevators - and, no, these Clients are not one of your 'one-percenters' - 
but  elevators are not listed in residential area of fire origin  statistics.

Here's my point Mr./Ms. AHJ: After forty years in the  sprinkler profession
, please do not tell me how to design fire  sprinkler systems. I will comply 
with whatever you mandate - just as long as it  is in the Code (i.e., 
"enforceable"). And please, stop  making reference to the NAHB (our "friends") 
- 
In my humble opinion, they should  be brought up on charges of crimes 
against humanity in an international  tribunal...In a residential sprinkler 
conference in Tucson some thirty  years ago (mandatory sprinklers were coming 
for 
multi-family dwellings) a local  NAHB rep stood up and stated: "If we let 
the government require sprinklers in  our homes, the next thing you know, they 
will be requiring us to wear seatbelts  in our cars". I rest my case.

Have a nice weekend, All.

Warm regards from snowy Santa Fe...

Jerry
[email protected]_ (mailto:[email protected]) 

Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.*
Santa Fe, New Mexico USA
(800) 503.1961 nationwide

*Licensed Fire Protection Engineers -  Architects/Inspectors/Fire 
Investigators:  AZ  CA  CO   NM  NV  NY  TX  UT  KS  MD  MS



In a message dated 1/30/2015 4:22:41 A.M. Mountain Standard Time,  
[email protected] writes:

Ron,

I know this is a sore subject that's been brought to a  boil with the 
recent loss of a significant building displacing some 1000  people in the 
middle 
of winter. As both a firefighter and code official I am  not alone, the 
public is also questioning this paradigm as well as the speaker  of the 
assembly 
in New Jersey. What happened in Edgewater was just a matter of  time. Its 
not all 13R's fault, combustible construction, pedestal  buildings..... a 
cocktail for disaster.

Steve said it best, local  building and fire officials have been handcuffed.

John Drucker - Mobile  Email
[email protected]<mailto:[email protected]>
Cell/Text  732-904-6823


"rongreenman ." <[email protected]>  wrote:

Hardly John. 13D and 13R are standards for different types of  buildings and
not stepping stones to better fire protection.


On  Thu, Jan 29, 2015 at 8:49 PM, John Drucker  <[email protected]>
wrote:

> Steve,  NFPA handed  them the weapon, 13R....
>
> As for IRC I subscribe to the life  safety part (13D/P2904) for dwellings,
> hey its you're  home.
>
> But multiple dwellings on pedestals where we start  counting stories at 
the
> pedestal ?, wood frame 5 stories up ?, and  then not fully sprinklered
> ?.....13R ?
>
>
> John  Drucker - Mobile Email
>  [email protected]<mailto:[email protected]>
> Cell/Text  732-904-6823
>
>
> Steve Leyton  <[email protected]> wrote:
>
> Yeah, how about  somebody file a lawsuit against the NAHB or all the
> homebuilders who  have lobbied and gotten return for the political 
patronage
> in the way  of suspended residential sprinkler requirements or other such
>  loopholes or relaxations?    This is dirty business, but it's the  only 
way
> that things area going to change.   Go to the Fire  Sprinkler Initiative's
> website and look for the page that has  "Sprinkler Requirements By State".
>  I realize this is off the  topic of Edgewater a bit, but it's outrageous
> how many state  legislatures have passed prohibitions against any 
ordinance
> or  adoptions.   They completely handcuffed local building and  fire
> officials ...
>
> I've been asked to consult on  projects where owners and/or architects are
> trying to get 13D accepted  instead of 13R, or 13R instead of 13.   I 
won't
> take the  jobs, but I'm offered one or more a month.
>
> SL
>
>  -----Original Message-----
> From: Sprinklerforum on behalf of John  Drucker
> Sent: Thu 1/29/2015 6:32 PM
> To:  [email protected]
> Subject: Re: 13D exterior  overhangs.
>
> Owen, agreed 13D does not require heads under  overhangs.  What I  am
> saying is what's to stop an adopting  agency from amending the standard ?,
> nothing.  Until a code or  standard is adopted it has no jurisdiction.
>
> In any case I  understand the value of 13D and P2904 hence why I supported
> their use  for amendments to R300 of the NJIRC.  The recent events in
>  Edgewater NJ may change how and when 13R is deployed despite the  
standards
> intent. People up there are really pissed, a second lawsuit  was filed 
today.
>
> John
>
>
>
> John  Drucker - Mobile Email
>  [email protected]<mailto:[email protected]>
> Cell/Text  732-904-6823
>
>
> [email protected] wrote:
>
>  John,
> Thank you for responding. It goes back to the intent of 13D, to  provide
> people 10 minutes to escape and for the system to be  affordable to 
install.
> If the place burns to the ground but everyone  escaped, the system worked
> 100% as intended. It drives me crazy as  inspectors come and go they add
> their personal wants and desires for  these systems without following 
proper
> procedure. 13D does not require  heads in exterior over-hangs.
> Owen Evans
> Former AHJ now 13D  designer and consultant.
>
> Sent from my iPhone
>
>  > On Jan 29, 2015, at 5:46 PM, "John Drucker - Home" <
>  [email protected]> wrote:
> >
> > Firstin,
>  >
> > The question is too vague to be answered. As an active AHJ  there are 
many
> > variables, adopted codes and standards, local  amendments, special
> > circumstances not addressed by the code,  variations, site approval 
trade
> > offs and on and on. In order to  answer the question each one of those
> has to
> > be  addressed. Believe it or not most AHJ's have an underlying need, 
real
>  or
> > imagined, that  they are trying to address. Keep in mind  cost is not 
one
> of
> > them since the AHJ doesn't (and  shouldn't) profit from requiring
> protection.
> > I'm not  defending this AHJ but you have to dig deeper.
> >
> >  Lastly I've said this time and time again, why are designers and
>  contractors
> > engaged in these arguments with AHJ's ?.    Convey your situation to the
> > beneficiary, that being the owner of  the property. If he/she disagrees
> let
> > them take up the  fight through appeal.
> >
> > John Drucker
>  >
> >
> > -----Original Message-----
> > From:  Sprinklerforum [mailto:
>  [email protected]]
> > On Behalf Of  [email protected]
> > Sent: Thursday, January 29, 2015 6:29 PM
>  > To: [email protected]
> > Subject: 13D  exterior overhangs.
> >
> > 13D does not require heads in  exterior over-hangs, such as a second 
story
> > over-hanging a  driveway. Can an AHJ apply 13 rules to 13D systems
> without an
>  > amendment and require heads in over-hangs 4' & greater?
>  >
> > Sent from my iPhone
> >  _______________________________________________
> > Sprinklerforum  mailing list
> > [email protected]
>  >
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  >
> >
> >  _______________________________________________
> > Sprinklerforum  mailing list
> > [email protected]
>  >
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>
>  
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--
Ron  Greenman
Instructor
Fire Protection Engineering Technology
Bates  Technical College
1101 So. Yakima Ave.
Tacoma, WA  98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700  (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,  WSAFM, WFC, WFSC

They are happy men whose natures sort with their  vocations. -Francis Bacon,
essayist, philosopher, and statesman  (1561-1626)

A problem well stated is a problem half solved. -Charles F.  Kettering,
inventor and engineer  (1876-1958)
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to