So sprinklers removed for NFPA 25 inspection procedures and dry sprinklers
can be replaced, but other sprinklers can't?  Even though the same people
are handling all of them?  I don't see how these exceptions make sense.  I'm
pretty much old school on most things but what would allow ANY sprinkler to
be replaced given the bucket of heads argument?

Bill Brooks

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Cahill, Christopher
Sent: Saturday, February 07, 2015 11:54 AM
To: [email protected]
Subject: RE: Relocate sprinklers with drops RETORT

Agree - here's my question where's the data or experience this is a problem?
For 15 years I was either the FPE for St. Paul or a sprinkler contractor.
In St. Paul I personally went to about 90% of the sprinkler activations and
as a contractor we were small enough I knew of everything we did.  Not once
did I have any reason to believe a false discharge was caused by a
repositioned head whether removed from it's fitting or not.  I have to
believe there were 10's of thousands of heads moved in this period.    

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Greg McGahan
Sent: Friday, February 06, 2015 8:59 PM
To: [email protected]
Subject: Re: Relocate sprinklers with drops RETORT

It sure seems like a waste of resources to me. 

Sent from my iPhone

> On Feb 6, 2015, at 6:49 PM, <[email protected]>
<[email protected]> wrote:
> 
> Like shipping, unpacking and installation only applies the proper and
necessary stress for the sprinkler to operate as intended. Or maybe the
engineering is so precise that the sprinkler can only stand the rigors of
being threaded into a fitting once and then it's useless. Or maybe there are
sprinkler manufacturers reps on the 13 committee that know how fragile and
un-robust sprinklers are? Why would you build something could only be
threaded in once? I'm glad they don't manufacture pipe or fittings.
> 
> Ron fletcher Sent from my iPhone
> 
>> On Feb 6, 2015, at 4:43 PM, John Denhardt <[email protected]>
wrote:
>> 
>> Mark - well said. I totally agree. 
>> 
>> Sent from my iPhone
>> 
>>> On Feb 6, 2015, at 6:29 PM, "Mark A. Sornsin, P.E."
<[email protected]> wrote:
>>> 
>>> My two cents is that it is not only the potential stress to the
sprinkler from removal/replacement, but the potential for damage during
handling.  This is especially true for QR sprinklers.
>>> 
>>> From the EOR perspective, I have them replaced with new regardless of if
it could be kept in a drop.
>>> 
>>> I understand there may be differing perspectives when you are in a
competitive bid that doesn't address the issue, or you have an owner griping
about every dollar spent.
>>> 
>>> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
>>> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
>>> http://www.kfiengineers.com
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum 
>>> [mailto:[email protected]] On Behalf Of 
>>> [email protected]
>>> Sent: Friday, February 06, 2015 4:05 PM
>>> To: [email protected]
>>> Subject: Re: Relocate sprinklers with drops RETORT
>>> 
>>> Good afternoon, All:
>>> 
>>> I thought a previous discussion revealed that currently IF the sprinkler
stays in the RC, weld-o-let, fitting, etc., then it can be  reinstalled if
the sprinkler has not actually been removed from the original
fitting/outlet.
>>> I believe the concern was the amount of 'stress' applied to the
sprinkler when trying to remove it - and possible damage resulting from the
'torque'.
>>> Previously, everyone seemed to be on board with this  approach.
>>> 
>>> Cordially-
>>> 
>>> Jerry
>>> [email protected]_ (mailto:[email protected])
>>> 
>>> *Jerry D. Watts, SFPE
>>> President & Co-Founder
>>> ACCENT FIRE ENGINEERING INT'L. Ltd.** Santa Fe, New Mexico USA
>>> (800) 503.1961 nationwide
>>> 
>>> *New Mexico Journeyman Sprinklerfitter Lic.  #08228
>>> 
>>> **Licensed Fire Protection Engineers -  Architects/Inspectors/Fire
>>> Investigators:  AZ  CA  CO   NM  NV  NY  TX  UT  KS  MD  MS
>>> 
>>> 
>>> 
>>> In a message dated 2/6/2015 2:04:42 P.M. Mountain Standard Time,
[email protected] writes:
>>> 
>>> Based on  the 2nd draft, this is what the 2016 language will say 
>>> unless it is  Successfully NITMAM ed
>>> 
>>> 6.2.1.1*
>>> When a sprinkler is removed  from a fitting or welded outlet, it shall
not be reinstalled except as  permitted by 6.2.1.1.1.
>>> 6.2.1.1.1
>>> Dry sprinklers shall be  permitted to be reinstalled when removed in
accordance with the manufacturer's  installation and maintenance
instructions.
>>> 
>>> A.6.2.1.1
>>> Sprinklers should be permitted to be reinstalled when the sprinkler
being removed from the system remains attached to the original fitting or
welded outlet, provided care has been taken to ensure the sprinkler has not
been damaged. Flexible hose connections are considered a fitting.
>>> In new  installations, where sprinklers are installed on pendent drop
nipples or  sidewall sprinklers prior to final cut-back, protective caps
and/or straps  should remain in place until after the drop nipple has been
cut to fit to the  final ceiling elevation.
>>> 
>>> This is my opinion only and does not  constitute the official opinion of
the NFPA.
>>> 
>>> Peter Schwab
>>> VP of  Purchasing & Engineering Technologies
>>> 
>>> Wayne Automatic Fire  Sprinklers Inc.
>>> 222 Capitol Court
>>> Ocoee, Fl 34761
>>> 
>>> Mobile: (407)  468-8248
>>> Direct: (407) 877-5570
>>> Fax: (407)  656-8026
>>> 
>>> www.waynefire.com
>>> 
>>> 
>>> 
>>> 
>>> -----Original  Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]] On Behalf Of 
>>> michael  G
>>> Sent: Friday, February 06, 2015 3:56 PM
>>> To:  [email protected]
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> I would have to agree with Richard,  He is not pulling  the head out of
the piping, the Boss of the sprinkler is taking no extra  strain and there
is no extra stress added on the sprinkler head its  self.  Only the piping
is being removed, cut threaded and  reinstalled.  We basically do this when
we install a system....
>>> 
>>> We  run the branch line, install a 0-2 and elbow, the drop and a head
with the  support ring installed already, so that when we do our initial
testing for  leaks, the drops are tested all the way to the sprinkler head.
The reason for  this is, 1) to eliminate the number of potential leaks at
the end of the job  while conducting the final pressure test. 2) if there is
a bad head or  something wrong, i.e.  cracked 1 x 1/2" RC, it is easier to
change it out  then, instead of over finished floor and product.
>>> 
>>> 
>>> Mike
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of Duane  Johnson
>>> Sent: Friday, February 06, 2015 3:44 PM
>>> To:  [email protected]
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> 6.2.1.1 (2013) When a sprinkler has been removed for any  reason, it
shall not be reinstalled.
>>> 
>>> 
>>> Duane Johnson
>>> Strickland  Fire Protection
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of  Richard Carr
>>> Sent: Friday, February 6, 2015 3:38 PM
>>> To:  [email protected]
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> If he is not pulling the head how is it a violation of  NFPA?
>>> 
>>> Richard Carr, SET
>>> Branch Manager
>>> Cox Fire Protection,  Inc
>>> 6555 Grace Lane.
>>> Jacksonville, Fl.  32205
>>> [email protected]
>>> 904-781-8227
>>> 
>>> 
>>> -----Original  Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of Duane  Johnson
>>> Sent: Friday, February 06, 2015 3:29 PM
>>> To:  [email protected]
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> The problem is, you won't find this in the standard unless  you 
>>> print out the ROC...
>>> 
>>> 
>>> Duane Johnson
>>> Strickland Fire  Protection
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of Duane  Johnson
>>> Sent: Friday, February 6, 2015 3:28 PM
>>> To:  [email protected]
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> Not permitted. There was a proposal submitted on the last  cycle to 
>>> allow this, but it was rejected.
>>> 
>>> 
>>> Duane  Johnson
>>> Strickland Fire Protection
>>> 
>>> 
>>> -----Original  Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of Art  Tiroly
>>> Sent: Friday, February 6, 2015 3:29 PM
>>> To:  [email protected]
>>> Subject: RE: Relocate sprinklers  with drops
>>> 
>>> I am having an argument with a contractor that is removing  heads 
>>> and drops then moving them to a new position. Sprinklers are QR less  
>>> than 5 years old.
>>> He is not removing the head from the drop or the 1x1/2  RC. He says 
>>> he is not reusing sprinklers just relocating them with the drop  
>>> nipple. He says this is standard practice.
>>> Does this violate 6.2.1.1? Do  not reuse sprinklers removed from the
system.
>>> 
>>> 
>>> Art Tiroly
>>> ATCO  Fire Protection/Tiroly
>>> 24400 Highland Rd CLE  44143
>>> 216-621-8899
>>> 216-570-7030  cell
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org _______________________________________________
>>> Sprinklerforum  mailing  list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org _______________________________________________
>>> Sprinklerforum  mailing  list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org _______________________________________________
>>> Sprinklerforum  mailing  list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org _______________________________________________
>>> Sprinklerforum  mailing  list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum  mailing  list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> 
>>> ____________________________________________________________________
>>> __ This email has been scanned by the Symantec Email Security.cloud 
>>> service.
>>> For more information please visit http://www.symanteccloud.com 
>>> ____________________________________________________________________
>>> __
>>> 
>>> ____________________________________________________________________
>>> __ This email has been scanned by the Symantec Email Security.cloud 
>>> service.
>>> For more information please visit http://www.symanteccloud.com 
>>> ____________________________________________________________________
>>> __ _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to