I agree sort of without a specific example.  I don't do a lot of FM work so I 
don't know of any place you can't comply with both. Less is not equivalent.  
Only the AHJ can determine equivalent. You don't have to comply with both if 
they conflict, you have to comply with NFPA 13.  Like Ron said two submittals 
will often work to make everyone happy when FM is more.  I get FM typically has 
more relevant data that often shows equivalency as far as the ability to 
suppress a fire.  But all the pictures and video in the world don't help if the 
AHJ sticks with particular NFPA 13 design over an FM design. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Thursday, February 12, 2015 7:28 AM
To: <[email protected]>
Subject: Re: NFPA 13 & FM Mix

But in some-storage cases you not comply with both with out using NFPA's 
equivalency approach. 

Sent from my iPhone

> On Feb 12, 2015, at 8:25 AM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> You are most likely legally obligated to provide the minimums of NFPA 13.  
> You may sign a contract to provide more, but not less.  FM or silly PE 
> requirements might be examples.  
> 
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> *Registered in: MN
> 
> 
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
> For
> 
> 
> -----Original Message-----
> From: Sprinklerforum 
> [mailto:[email protected]] On Behalf Of 
> Gregg Fontes
> Sent: Wednesday, February 11, 2015 6:03 PM
> To: [email protected]
> Subject: NFPA 13 & FM Mix
> 
> I have a quick question that I need a fast answer to.  Where is it in NFPA 13 
> 2013 Edition that you cannot mix the two design standards?   (I.E. you either 
> design per NFPA 13 or FM Global. You cannot pick and choose.)
> 
> Thanks,
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> 209-334-9119
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to