NFPA #13 is not based on IF there is a a fire - it is based on WHEN there
is a fire.....That has been hammered into my head since I got in this
industry...

WHEN there is a fire in that space - in this case the cooler, what happens?

The IBC is clear - if it is attached (by definition within the IBC) to a
protected building then sprinklers are required.....We have seen the
aftermath of multiple compressors catching on fire inside coolers/freezers
- so fires do happen in them.


Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Tue, Mar 10, 2015 at 7:10 AM, Matthew J Willis <[email protected]>
wrote:

> Also,
>
> Lest we forget, the materials used in the construction of these "Boxes"
> help a fire along regardless of the contents.
>
> R/
> Matt
>
> Matthew J. Willis
> Project Manager
> Rapid Fire Protection Inc.
> 1805 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Cell-605.391.2733
> Fax:-605.348.0108
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Cahill,
> Christopher
> Sent: Tuesday, March 10, 2015 6:07 AM
> To: [email protected]
> Subject: Re: exterior cooler/freezer
>
> Its called a backdraft. Look it up or watch the movie. Yes it can burn.
> Also be careful with statistics. One can show any given fire is highly
> unlikely. Yet they still happen on a regular basis.
>
> Chris Cahill
> Fire Protection Engineer
> Burns & McDonnell
> [email protected]
> 952-656-3652 Todd - Work wrote:
> I went to the jobsite yesterday to get the full scoop. This is a
> restaurant in a strip mall. In back, there will be two boxes approximately
> 9 x 16 x 8(h). One will be liquor storage, which needs to have an inside
> access. This will be conditioned space and we will run 2 heads off the
> existing. The second is a combination freezer/cooler with the front 10 ft
> cooler and the back 6 ft freezer. That adds complications. You would now be
> looking at a 2 head dry system. The owner is considering eliminating the
> inside access for that box. They have contacted the AHJ to see if that
> would eliminate then need for sprinklers.
>
> My next question is on fire history in this type of box. By design, it
> will be pretty much air tight to preserve the temperature. Given the size
> of the space, would there be enough oxygen inside to sustain a fire that
> would expose the main building? Is there any history of this type of fire?
>
> Sent from my iPad
>
> > On Mar 10, 2015, at 6:35 AM, John Drucker <[email protected]>
> wrote:
> >
> > Bill,  like the recent blue dress experiment our eyes see what we want
> them to. Fires, what fire ?
> >
> > John Drucker - Mobile Email
> > [email protected]<mailto:[email protected]>
> > Cell/Text 732-904-6823
> >
> >
> > Bill Brooks <[email protected]> wrote:
> >
> > Sometimes there are interpretations and sometimes misapplications.  An
> > intelligent interpretation is a help to a designer, a misapplication
> > can be a dangerous thing.  I'm not sure which one is being referenced
> here.
> >
> > Bill Brooks
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]]
> > On Behalf Of Charles Thurston
> > Sent: Monday, March 09, 2015 5:50 PM
> > To: Cahill, Christopher; [email protected]
> > Subject: Re: exterior cooler/freezer
> >
> > Hello Christopher,
> >
> > That is what the AHJs around here look at it as. They say the closed
> > cooler door is like a fire door and no sprinkler needed. They even
> > told a building owner of he left the "decorative roof" off a 1500 sq'
> > cooler outside the building it did not have to be sprinklered.
> >
> > Monday, March 9, 2015, 11:16:43 AM, you wrote:
> >
> >> Hold on a second, there could be a fire wall between the two creating
> >> separate buildings, lol.
> >
> >> Chris Cahill, PE*
> >> Associate Fire Protection Engineer
> >> Burns & McDonnell
> >> Phone:  952.656.3652
> >> Fax:  952.229.2923
> >> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to