At several aircraft hangars in a previous life because 409 used to contain 
testing requirement.  It may still.  We used a combination of weirs with 
automatic sluice gates and EPDM effluent ponds to satisfy that airfield, the 
local sewer authority and the EPA (state and fed).  We did not do these on base 
but I have heard it, or a similar strategy, is employed in sensitive coastal 
areas.

Normal circumstances; pond sits open to the sky and storm drainage, hangar 
drains thru OWS to sanitary.  Apron also drains to OWS IF they are fueling - 
designate an area or it gets absurd - otherwise it goes to storm.

Event involving AFFF occurs; first weir shuts to OWS and opens to effluent 
pond, at the same time second weir shuts off pond from storm and contains all 
effluent in pond until local sewer authority is informed of coming discharge to 
sanitary.  They may dictate rate of flow as it is likely to contain petroleum 
products or worse and AFFF depletes oxygen in streams as well as settling 
basins.

Actuaries for an unnamed insurance company determined likelihood of two fires 
at same airfield in same containment period (assumed two days) to be ten to the 
negative 11th.

Think flat slopes with no perched pipes - agitated AFFF foams up and becomes 
difficult to contain.

Examples: Black oval @ 40°00'18.05" N  82°54'00.89" W.; black rectangle @ 
39°06'34.24" N  84°24'58.03" W



ROBERT HOLLAND Jr. AIA, CDT, LEED AP, PMP
ARCHITECTS / ENGINEERS / INTERIOR DESIGNERS
7400 West Campus Rd.   Suite 150   New Albany, OH  43054   www.shremshock.com
t 614 545 4550 x 286     f 614 545 4555     [email protected]
Please consider the environment before printing this e-mail.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, March 11, 2015 1:29 PM
To: [email protected]
Subject: Foam system testing

Has anyone had to test a foam sprinkler system where it was required to contain 
the discharge from the test and not let it flow into sewers or other site 
drainage systems?  Basically it had to be contained and removed from the site?

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to