NFPA 24 says minimum 6" if you have fire hydrants.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
[email protected]
904-781-8227


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote
Sent: Friday, March 20, 2015 3:11 PM
To: [email protected]
Subject: Minimum size od Underground supply.

I seem to remember somewhere in NFPA 13 that the minimum size for U/G piping 
was 6" for ordinary hazard systems. Now someone wants chapter and verse and 
I'll be darned if I can find It.