It's a solid pile, this I know.    If a fire is working outside of the
boxes it could involve them and they would behave predictably I think -
they'd spill contents at some point but contents are mixed, so I'm not
thinking free-flowing or anything like that.  The plastic tops become a
factor if the fire starts INSIDE of a box, especially a lower one.  Not
sure what else to do about it except call it Group A (which it's most
certainly not) or upgrade it to ESFR arbitrarily.  Shielded commodity
would be Extra Group II, so you could arbitrarily upgrade to a .40
density if you're not there already as a Class 4 solid.

I don't know - you're the PE fer cryin' out loud ...

SML - No letters




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Roland Huggins
Sent: Wednesday, March 25, 2015 1:50 PM
To: [email protected]
Subject: Re: PODs Storage

Would that allow the plastic top as referenced earlier?  

NFPA 13 has identified that LARGE containers of household storage is not
addressed by the classification section.  If memory serves, the plastic
roof derailed any discussion on smaller containers.  Naturally there is
nothing to quantify how large is too large.




Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Mar 25, 2015, at 1:09 PM, Steve Leyton <[email protected]>
wrote:
> 
> We've used Solid Pile, Class IV in the past so long as the business 
> has a strongly worded contract prohibiting aerosols, 
> flammable/combustible liquids and haz-mats.
> 
> SL
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to