I have some contractors that use the flexible fittings regularly. I
just have them give me the datasheet for the brand they want and calc it
out. If I have time, I will also run a set of calcs and compare to
Flexhead which usually has lower friction losses. If one gives smaller
pipe size over the other, I let them decide what they want, then finish
the drawing based on that. But, you can really get caught off guard if
you don't figure some of these friction losses properly. I have seen
some lower cost brands that have something like 50' of equivalent loss.
That can be a real problem.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 3/30/2015 8:52 AM, Todd - Work wrote:
I am running into the new generation of flexible fittings which I understand a
significantly cheaper but have significantly higher friction loss. Has anyone
had problems with these? I'm always a little leery of the cheaper alternative
until it proves itself.