NFPA 13 (2013)

8.5.5.4 Closets. In all closets and compartments, including
those closets housing mechanical equipment, that are not
larger than 400 ft3 (11.33 m3) in size, a single sprinkler at the
highest ceiling space shall be sufficient without regard to obstructions
or minimum distance to the wall.

On Thu, Apr 9, 2015 at 6:42 AM, Matt Grise <[email protected]> wrote:

> I looked through the archive, but I could not find any definitive answers
> on this:
>
> I have a building protected to 13 (not 13R) that has small (200 cubic
> foot) mechanical closets that are packed full of HVAC equipment. Is there
> any guidance in the codes or printed references that discuss allowances for
> obstructions in small closets for 13 systems? I am familiar with the 400
> cubic foot allowance in 13R, but it still seems like it would be
> unreasonable to have 3 or 4 sprinklers in these very small spaces.
>
> Thanks,
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>