A rural detention center I worked on found one inmate that did not fear the
rule, activated the sprinkler next to the upper bunk and sent him to the
floor when the fire pump doused him with pond water. Word spread > don't
mess with the sprinklers.
Art
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, April 16, 2015 10:40 AM
To: [email protected]
Subject: RE: Type of fire protection system for detention centers RETORT

Nadeem,  just to expound further on Jerrys use of quotations around "tamper
proof:"

Institutional sprinklers are designed to prevent occupants form using them
for self-harm, such as hanging. They CAN be somewhat more resistant to
tampering than typical non-institutional sprinklers.  But they are not
tamper-proof, per se.  If an occupant wants to damage or activate an
institutional sprinkler, they will be able to find a way; it will just be
more difficult than a standard sprinkler. There are no truly tamper-proof
sprinklers.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Thursday, April 16, 2015 9:27 AM
To: [email protected]
Subject: Re: Type of fire protection system for detention centers RETORT

Ladies/Gentlemen (and Roland):

Preferably wet-pipe fire sprinkler system in heated (40+ F.)  areas -
dry-pipe system in unheated areas..."Institutional" sprinklers
("tamper-proof") in areas accessible to 'residents' - in areas
non-accessible, quick-response sprinklers in all Light Hazard areas...

Best to All-

Jerry
[email protected]_ (mailto:[email protected])

Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd.
Santa Fe, New Mexico USA
(800) 503.1961 nationwide



In a message dated 4/16/2015 12:18:10 A.M. Mountain Daylight Time,
[email protected] writes:

Dears

Can anybody advise me the type of fire protection  system required for
detention centers.


--
Regards

Nadeem Ahmed
Mechanical  Engineer
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to