Thanks Roland and Travis. No wonder I felt squeamish about this. I don't
have a lot of experience with 'going up and to the left' of the LH thru EH
curves. Good eye on the listing Travis-- the one I just looked at shows SR
for 200F at 20 x 20!!!

Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Thursday, April 30, 2015 9:51 AM
To: [email protected]
Subject: Re: QR Reduction and single points on the Density/Area Curves

But don't you have to go by the data sheets for the sprinklers?  It only 
lists 20x20 at 40 gpm for light hazard.  I don't see where the data 
sheet says I can apply a lower flow for 20x20 spacing

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 4/30/2015 7:46 AM, Roland Huggins wrote:
> Since you picked 2000 sf based on 5 EC sprinklers, you can NOT reduce it
due to the 5 sprinkler minimum.  SO you go back to your 3,000 sf at .06,
reduce it to a minimum of 1800sf but exceed it since you're back at 2000 sf
due to the perfect 20 x 20 of your EC coverage and 5 sprinkler minimum.
Cutting it back to 18 X 18 would not meet the 1800 so to get a perfect
score, back to the area/density curve and pick 2700 sf at .076.
>
> Roland
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>
>
>
>
>
>> On Apr 30, 2015, at 6:39 AM, Brad Casterline <[email protected]>
wrote:
>>
>> Dear Forum,
>>
>>
>>
>> I would appreciate feedback on the technical (or moral) correctness of
the
>> following scenario:
>>
>>
>>
>> NFPA 13 (2010 or 2013), Light Hazard, Ceiling smooth and flat at 10'-0"
AFF.
>>
>> Sprinklers= QR, EC, 200F, K=11.2 at 20' x 20'.
>>
>>
>>
>> Choose .07/3000 for starting point from L.H. curve. Apply Q.R.
Reduction--
>> 3000 x .6 = 1800 ft^2.
>>
>> Length of operating area = 1.2 x SQRT(1800) = 50.91 ft., / 20 = 3
hds/line.
>> 1800/400= 6 hds operating.
>>
>> Q=400 x .07 = 28 GPM. P=(28/11.2)^2 = 6.25 PSI raise to EHP= 7 PSI.
>>
>>
>>
>> Since (5) is the minimum number of operating heads for Density/Area, is
it
>> OK to 'choose' the density based on 3000 ft^2, or would it be more
righteous
>> to 'use' the density based on 5 x 400 = 2000 ft^2, .09, then reduce the
>> operating area to 2000 x .6 = 1200 ft^2?
>>
>>
>>
>> thanks,
>>
>>
>>
>> Brad Casterline, NICET IV
>>
>> Fire Protection Division
>>
>>
>>
>> FSC, Inc.
>>
>> P: 913-722-3473
>>
>> [email protected]
>>
>> www.fsc-inc.com
>>
>>
>>
>> Engineering Solutions for the Built Environment
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to