That would be a tough sale to a literal AHJ since you said Sales Counter in the 
area.  The reality is that mercantile is one of the few places that 13 does NOT 
base the classification on actual contents  but on what MAY be there in the 
future.  This must have been done due to the high rate of changes in typical 
stores.  As such, it you have a steel ball bearing manufacture that also sells 
their product in a building out front, the metal 4 ft shelves with nothing but 
metal boxes with steel ball bearings would be an OH design.  Now I may be out 
in right field (I’ll leave the left field for congress), but I’d be whipping 
out my PE and having a discussion about the why’s and what’s along with some 
kind of assurance that any changes will actually be evaluated beforehand and 
sprinkler modifications made if needed like the IFC requires but no one does.

So - how well do you dance?

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 30, 2015, at 9:10 AM, Todd - Work <[email protected]> wrote:
> 
> I am working on a project where the customer is constructing a small showroom 
> to display electrical fixtures and similar products. Approximately 60% of the 
> space will have these displays and the other 40% will be sales counter. Their 
> "store" is located in the another part of the building so there will not be 
> any aisles with parts, etc in this space. Would this space be considered 
> mercantile? 
> 
> Unfortunately we have a marginal water supply, are at the diagonal opposite 
> side of the facility from the riser and have a dry system with no option of 
> converting to wet. Consequently, I can't get OH2 to work hydraulically. 
> 
> Thoughts?
> 
> 
> 
> 
> Sent from my iPad
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to