Probably. It really needs to be investigated further. You may be correct about being fed from the domestic water system (and not just glued to the ceiling). The requirement is a Code and possible AHJ issue that should be looked into.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2] On Mon, May 4, 2015 at 9:50 AM, [email protected] <[email protected]> wrote: Good morning gentlemen, I am looking at a 2 story office building circa 1995 with a small 2 story lobby that is separated from the rest of the building with fire doors. This lobby has sprinkler heads. There is no riser and no flows or tampers that anyone who has been there 9 years knows of. Each floor is only 12,500 sf. I am assuming that these were added off of the cold water line and are not required. Is that a poor assumption? ᐧ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org