I got a flow test with a much higher pitot than residual due to a 51 Ft.
elevation change.

Art
ATCO

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Wednesday, May 13, 2015 1:41 PM
To: [email protected]
Subject: RE: Flow test - Playpipe w/ 1 1/4" Tips

Also, I think you missed what Art said, he was referring to the Pitot
pressure in excess of the residual, and actually, I believe that can happen
when testing with a Playpipe due to the increase in velocity. Or I could
have just made that up........ steve. :-0 Mark at Aero
602 820-7894

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Wednesday, May 13, 2015 10:22 AM
To: [email protected]
Subject: Re: Flow test - Playpipe w/ 1 1/4" Tips

Technically it can happen.  When the supply drops, additional supply pumps
kick on, creating a residual pressure greater than the static.  No guidance
in NFPA 24 in how to address so if one applies a literal read, you
extrapolate toward infinity. It's in the works to address.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On May 13, 2015, at 9:46 AM, Art Tiroly <[email protected]> wrote:
> 
> How did you get a pitot higher than the residual?  Can't happen. Gage
error?
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to