http://www.mail-archive.com/sprinklerforum%40lists.firesprinkler.org/msg4094
9.html

David,

I found the above link in the archives. There is no definitive answer but
the responses got me thinking that if the use of a different commodity
classification were allowed the question would then be "OK, what, Class II?"

I think in order to see the effect of fire resistance treatment, the same
full scale tests that quantify Quantity, Combustibility, and Heat Release
Rate of the non treated commodity, for classification purposes, would have
to have been done to the treated commodity.

Perhaps I am all wrong but when I think 'Combustibility' I think Fire Growth
Rate, for instance, if LH is a "t^2 Slow" fire then OH1 might be a "t^2
Medium" fire, etc., so 'resistance' would only make the growth rate slower,
but eventually the water application rate required for control or complete
extinguishment would be based on the Quantity and HRR of the non-treated
commodity... or not! :) !

Sorry this is of no help, but I hate to see anyone out there flapping in the
Forum Breeze.

Brad  

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of David Bitton
Sent: Thursday, May 21, 2015 11:27 AM
To: [email protected]
Subject: "Fire Resistant" Foam

Hello,

 

I am looking at a warehouse with rack storage of foam used for seat cushions
on mass transit systems (rail and bus).  To be used in such applications,
the foam must be tested for smoke generation (ASTM E662), rate of heat
release (ASTM E1354), horizontal burn test (DOT FVSSS 302), and vertical
burn test (FAR 25.853 (2)).  The product in question was tested and approved
in accordance with these requirements.  My question is does any of this
permit the use of a commodity classification other than expanded Group A
plastic?

 

Thank you.

 

David Bitton, ing.

Les services de prévention des sinistres Quest inc.

Quest Loss Control Services Inc.

5100, rue de la Savane, bureau 200

Montréal, QC H4P 1T8

(514) 341-4545

www.questlosscontrol.com

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to