Hello rongreenman,

Oh I know why, Just the guys doing the insulation did  it the other way, Now 
they want a code reference before they will change it. Said they have been 
doing it that way for years and nobody ever said anything.  AHJ is gonna make a 
"friendly stop" by and "happen" to discover it at this point.

Thursday, June 4, 2015, 2:59:39 PM, you wrote:

> The vapor barrier over the piping is to keep the insulation from getting
> under the pipes and insulating it from heat infiltration from the room
> below. The batts over tented spaces are used because it is easier to keep
> them in place at the desired thickness over the pipes, the most important
> place, than the blown stuff.

> On Thu, Jun 4, 2015 at 11:40 AM, Charles Thurston <[email protected]>
> wrote:

>> Hello Jeff,

>> Hard to do in an assisted living facility, Gotta have wet pipes to get the
>> water to the rooms.

>> Thursday, June 4, 2015, 1:38:40 PM, you wrote:

>> > Don't we know it.  The details and longevity is critical.  Best to
>> > avoid the areas subject to freezing.
>> > Jeff Feid

>> > -----Original Message-----
>> > From: Sprinklerforum
>> > [mailto:[email protected]] On Behalf Of
>> Scott A Futrell
>> > Sent: Thursday, June 04, 2015 11:06 AM
>> > To: [email protected]
>> > Subject: RE: Insulation of pipe in attics

>> > "Tenting" can be problematic regardless of where the vapor barrier is
>> located.

>> > The tent must remain intact for the life of the structure and by
>> > intact I mean free from being disturbed by anyone in the space
>> > (electrical, cable, satellite, other) and if there are holes or gaps
>> > from the install, settling of the insulation, or someone in there,
>> > the cold air gets in.  The cold also can be drawn in through holes
>> > or gaps by mechanical equipment creating a negative in the structure
>> > such as bathroom exhaust fans, kitchen exhaust fans, furnaces,
>> > fireplaces, and so on and a combination of those all operating at
>> > the same time makes the condition worse.

>> > Be careful when you go this route.

>> > Scott
>> >
>> > Office: (763) 425-1001 x 2
>> > Cell: (612) 759-5556

>> > -----Original Message-----
>> > From: Sprinklerforum
>> > [mailto:[email protected]] On Behalf Of
>> Charles Thurston
>> > Sent: Thursday, June 04, 2015 10:54 AM
>> > To: John Denhardt
>> > Subject: Re: Insulation of pipe in attics

>> > Hello John,

>> > Thank You.  Those are good, but they are blowing in the insulation
>> > in the rest of the ceiling so they do not show the plastic sheeting
>> under the batts of insulation.

>> > Thursday, June 4, 2015, 11:22:51 AM, you wrote:

>> >> Look at the NFPA Research Foundation report that covers insulation for
>> >> sprinkler piping.  It has some very good details and pictures.

>> >> John

>> >> -----Original Message-----
>> >> From: Sprinklerforum
>> >> [mailto:[email protected]] On Behalf Of
>> >> Charles Thurston
>> >> Sent: Thursday, June 04, 2015 11:27 AM
>> >> To: [email protected]
>> >> Subject: Insulation of pipe in attics

>> >> Hello Sprinklerforum,

>> >>   I have a project where they are using blown insulation in the attic.
>> >> Per the diagram I have seen many times I showed plastic sheeting
>> >> draped over the pipe and batt insulation on top of the plastic. The
>> >> insulation installers put the batt on the pipe and plastic over that.
>> >> Looking for the code section that describes it with the plastic under
>> >> the pipe. I looked at 13 which refers back to 13D that I do not have
>> >> here, Any help on the section with the diagram?




>> > --
>> > Best regards,
>> >  Charles                            mailto:[email protected]

>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> >
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> >
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> >
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



>> --
>> Best regards,
>>  Charles                            mailto:[email protected]

>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]

>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







-- 
Best regards,