We have a project where the overall building is broken into separate buildings with the use of fire walls to create the area separations.

As these are "separate buildings," am I correct to assume that you can have one of these protected via NFPA 13 and the others per NFPA 13R? We have a project with "five" buildings under one roof. They have the fire walls going all the way through to create the area separations. It seems in Building 1, the architect is using the sprinkler allowance to get the floor area (24k sq ft with Type V-A construction). Bldgs 2-5 are all under the 12k sq ft for Type V-A construction.

The other issue to question is fire area and required fire flows. If Bldg 1 is protected with a 13 system, I can apply the sprinklered building reduction and get our fire flows into what is required. This particular AHJ will only all a 50% reduction in fire flows, and only for a 13 system. 13R gets no reduction. The other buildings have a site fire flow requirement that is consistent with our flow test, without any reductions.

Basically, I am looking for opinions to see if this reasoning makes sense. Yes, there should be an FPE involved, but unfortunately, one is not involved at this point.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to