FUNDAMENTALLY disagree (with all due respect).   Accessible as in,
accessible for occupancy or storage?   Or accessible as in, I can stick
my head up there.  The latter does NOT require sprinkler protection,
which I think is the point of this query.

SML





-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Roland Huggins
Sent: Friday, June 19, 2015 11:05 AM
To: [email protected]
Subject: Re: Condealed Space Access definition

yes and yes

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jun 19, 2015, at 10:52 AM, <[email protected]>
<[email protected]> wrote:
> 
> Happy Friday Forumites
> I'm looking for clarification/definition for intent in NFPA 13 12010
Edition section 8.15.1.2.2 Concealed spaces of noncombustible and
limited-combustible construction with limited access and not permitting
occupancy or storage of combustibles shall not require sprinkler
protection.
> 
> First question - Does the space above the suspended ceiling of an
office occupancy, from the ceiling to the roof deck above meet the
definition of "concealed space"?
> Second question- Does this same suspended ceiling (either acoustic
tile or sheetrock tile) meet the definition of "limited access"?
> 
> Mark at Aero
> 602 820-7894
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to