John,

You're on the mark, what good is an exercised BFP if the hydraulics degrade, 
especially if the degradation results in being below the demand curve.  

John Drucker

 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Denhardt
Sent: Tuesday, June 23, 2015 9:21 AM
To: '[email protected]'
Subject: RE: BFP_Compare_Roland

FWIW - Years ago with an older backflow, we did a forward flow test and 
measured pressure drop across the device.  6" backflow, 500 gpm flowing and a 
38 psig loss.  Investigation showed this backflow had issues.  Once cleaned and 
repaired, all was normal.

I always thought the intent of the 25 requirement was to check the pressure 
loss across the device and compare to manufacture's data.  But I was quickly 
corrected in discussions with 25 committee members.  All they were looking for 
was to "exercise" the device.  No pressure loss measurements were required.

John

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Todd - Work
Sent: Tuesday, June 23, 2015 6:21 AM
To: [email protected]
Subject: Re: BFP_Compare_Roland

John, That sort of is my point. I have heard of BFP issues with ITC flows as 
well. My question is what new problems are we going to learn about at full flow 
that would not show up at ITC or 2" drain flows?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Tue, Jun 23, 2015 at 5:59 AM, [email protected]
<[email protected]> wrote:
Todd, I can add cite two instances where the first check of a BFP was too tight 
at single head flow (low flow) causing the waterflow switch to cycle therein 
never reaching the retard and never tripping the alarm panel. This was found by 
conducting a proper waterflow test thru the ITC with the smallest K head in it.
The BFP manufacturer was contacted and as happens often enough, the by the way 
answer comes out about using a special first check for low pressure water 
systems. Once swapped out worked like a charm. The moral to this story, never 
ever test a waterflow switch by simply removing the cover and moving the vane 
arm by hand.

We do forward flow BFPs per 25 and have yet to see one hang. But I'm sure that 
day is coming.

John Drucker - Mobile Email
Assistant Construction Official
Fire Protection Subcode Official
[email protected]<mailto:[email protected]>
Cell/Text 732-904-6823


Todd - Work <[email protected]> wrote:

I wouldn't mind hearing this as well. I would think that between inspector's 
test flows, 2" drain flows and annual backflow preventer tests (required by 
states), that the health of the BFP would be sufficiently determined. Of course 
in Light/Ordinary Hazard situations, the 2" drain could discharge system 
demand, so the requirement would be met. Perhaps a full flow as part of an 
acceptance I could understand. Have there been any instances where there has 
been a backflow preventer failure at full flow and not at a lower flow?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com<http://www.fpdc.com>
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Tue, Jun 23, 2015 at 1:55 AM, [email protected]
<[email protected]> wrote:
Something I have failed to understand, and would appreciate if someone can 
enlighten me.

The forward flow test is required at the full system demand, presumably to 
check the operation of the BFP. If the test shows that the BFP will open at 
system demand, what guarantee is there that it will open at a lower flow. I 
would think higher the flow, greater the force and easier to open the check 
valves. Or am I missing something?

Tony

----- Original Message -----

 From: "Brad Casterline" <[email protected]>
To: [email protected]
Sent: Monday, June 22, 2015 10:42:17 AM
Subject: RE: BFP_Compare_Roland

Hello Forum,

Two weeks ago I said:

"I fixed it and compared the results for a wide range of flows to the results 
in Roland's article and I will never bad-mouth Hazen, Williams, or Roland again 
:)."

Here is a summary of the more exhaustive comparisons for the 2" and 2 1/2"
Main Drain scenarios:

https://www.dropbox.com/s/1tqp42gqdpxum04/BFP_Compare_Roland.pdf?dl=0

and here is the link to the issue of Roland's article:

http://digital.turn-page.com/i/127056-may-2013

I added (5) quantities to each calc:

1) velocity
2) HW pf/ft
3) DW pf/ft
4) HW va eq len
5) DW va eq len

Looking at 4) and 5) you might see why I said, "My concept of K-Value and Pf 
and equivalent length being proportional to v^2 was exactly backwards."

I hope a Forumite or two finds this kind of thing as interesting as I do!!!

Thanks,

Brad Casterline
AFSA Designer Member and SET




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to