Another consideration is wind.  We (Dayton, Ohio) have seen several
ordinary apt. buildings with wet pipe freeze/breaks at the second floor
and third floor levels of three story buildings with full attics, where
the pipe was installed in an INTERIOR wall between well heated
apartments.   Exterior night temps were around 10F, but wind had been
blowing 15 to 20mph for two days.  Attic portion of the systems were
just fine, but the interstitial wall spaces were apparently not as well
protected from the wind event. 

Andrew Steele


-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Brian Harris
Sent: Tuesday, July 07, 2015 8:13 AM
To: [email protected]
Subject: RE: Attic Insulation

Allan-
Thank you very much, exactly what I was looking for!

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
AKS-Gmail-IMAP
Sent: Tuesday, July 07, 2015 12:15 AM
To: [email protected]
Subject: Re: Attic Insulation

For starters the ratio between R attic over R inside (the resistance
ratio) must be greater than the ratio between 40F - min. outside temp
over min. indoor temp - 40 F (the driving force ratio).  R attic is the
R value between the pipe and the attic. R inside is the R value between
the pipe and the heated space. For example if it is -10 F outside and 50
F inside then the temp ratio (the driving force ratio) is 60/10.
Therefore the R attic must be at least 6 times the R inside. 

This direction assumes there is no outside air leakage that introduces
outside air into the space under the insulation where the pipe is. The
40 F number is the minimum temperature for the pipe. The 50 F number is
a judgement you make for how cold the indoor temperature will be when
the going gets tough. So make a reasonable judgement. Obviously it might
be a bad judgement to assume normal indoor heating conditions. A
building where there is staff on hand to maintain some heat most of the
time or be able to drain down is different from a vacant building where
the residents are out of town for a season.

The R inside is the R value between the pipe and the heated space. You
must make a reasonable estimate for that value without omitting any
factors because omissions sway your final result in the wrong direction.
Insulating materials between the pipe and the heated space slow down the
heat transfer to the pipe. You want to make sure the heat transfer into
the pipe is faster than the heat transfer out of the pipe. That is what
this ratio comparison build down to.

This simplistic direction assumes the attic temperature is the same as
the outside temperature. You might think that may not be the case but in
a very well ventilated attic that might actually be the case right near
the attic vents. So again you need to make a judgement call. Also keep
in mind how easily the insulation installation could get screwed up
during installation and afterwards. There also must be a vapor barrier
between the heated space and the R attic insulation.

Get your minimum outdoor design temperature from a published source
intended for heating system design referenced by the building code. The
minimum temperature is probably lower than you think it might be.

Allan Seidel
St. Louis, MO    


> On Jul 6, 2015, at 1:01 PM, Brian Harris <[email protected]>
wrote:
> 
> Can someone point me in the right direction to determine what the
minimum R value is required to protect steel  pipe in an attic in SC ?
> 
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to