Based on the description it seems like the plastic is packaging, and it would 
fall under 5.6.3.3.2 and 5.6.3.4.1 (NFPA 13 2013) potentially, in which case it 
would be Class III or IV?
________________________________________
From: Sprinklerforum <[email protected]> on behalf 
of S & C Conlin <[email protected]>
Sent: Friday, July 31, 2015 1:52 PM
To: [email protected]
Subject: Exposed Nonexpanded Plastic Container

Involved with this project where the warehouse and the palletized storage
areas contain skids of exposed plastic pails containing non-combustible
solids.  I have recommended designing/upgrading the existing system to
protect a Group A Plastic.  I had the insurer tell me that the warehouse
commodity is a Class III and Class IV.  I am miffed.



Does anyone have any rationale why an exposed nonexpanded HDPE pail/bucket
(5 gal and 2 gal), containing a non-combustible solid would be considered
anything other than an Gr A?



Thanks in advance.

Sean

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org