Todd,

I don't believe Open Grid Ceiling rules will apply. The material can't be
any thicker than the least dimension of the opening. 
If it is a wood frame material like 2x solid wood then you will have an
obstruction to spray pattern to worry about. Once you get all the
information on the slatted ceiling solutions will be easier.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Todd - Work
Sent: Wednesday, August 19, 2015 8:10 AM
To: [email protected]
Subject: slatted ceiling

I am working on a project with a slatted ceiling in a wide corridor. The
ceiling construction is a fire rated wood and is considered non conbustible.
There is a 2' wide sheetrock soffit around the perimeter and the slatted
area is approximately 6 ft wide down the middle. The space above the ceiling
is non combustible and would not normally require sprinklers. The FM has
raised a question if sprinklers below would operate given the openings (I am
trying to get the dimensions of the openings and the slats). I did not see
anything in 13 addresses this. Am I missing something? Thoughts?

Sent using CloudMagic
[https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to