I agree with Todd, one other consideration, I would recommend that the fire
pump be tested to assure that it is performing per factory specifications
from churn to 150% of it rating. Once you assured yourself that the pump is
performing within spec I would use the flow and psi results to design the
new system.
Thanks.
Ed Cyr

On Mon, Sep 14, 2015 at 3:28 AM, Todd - Work <[email protected]> wrote:

> It depends on the arrangement. If the pump feeds a yard system including
> hydrants and sprinklers, then the pump test is the best way. If the
> hydrants are
> fed before the pump suction, that creates an issue of hose demand. In a
> perfect
> world, you would have a current hydrant flow test and use the pump test to
> determine the pump curve. You would start the calc at the hydrant flow
> test,
> take the hose stream demand from the hydrant and run the net flow through
> the
> pump. However, this is not a perfect world. Sometimes you are only given a
> pump
> test to work with. If that is the case, I look for the most demanding
> point past
> the discharge and leave a larger gap in the calc than normal.
>
> Sent using CloudMagic [
> https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
> On Sun, Sep 13, 2015 at 10:08 PM, [email protected]
> <[email protected]> wrote:
> When we have a project to replace or modify the sprinkler system in a
> building that has a fire pump, I have always been of the opinion that I can
> get a better water supply test by doing a fire pump test than I can get
> from a hydrant test. With a fire pump test, I have the pressures and flows
> for my new sprinkler system at the fire pump discharge. Any opinions?
>
>
> *Success Through Code Compliance*
>
> *Rahe Loftin, PE *
> *Regional Fire Protection Engineer*
> *General Services Administration*
> *Region 7 - TX, OK, NM, AR, LA*
> *Facilities Management & Support 7PMC*
> *c - 817-371-3102*
> *o - 817-978-7299*
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to