By spacing them at no less than 8 ft. No being a SA (well too much of one) but that is simply one of the annoying limits on ESFR. If close to 8 ft, try a staggered pattern (like often seen in days gone by).
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Sep 15, 2015, at 5:31 AM, Lamar Vaughn <[email protected]> wrote: > > I need some help with this, I find in NFPA 13 (2013) chapter 8 acceptable > ways to use baffles between close spaced heads but do not find this > language with regard to ESFR sprinklers. Is it not acceptable to use > baffles on these heads? And if not, how do you deal with less than 8 ft. > spacing? Thanks for your input. > > Lamar Vaughn, SET > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org