Devil's advocate. The code says there can be not control valve in the FDC
line (itself). It also has to be downstream of the check valve that
separates the source from the system so you don't pump a loop back to the
pumper. I don't recall off the top of my head anything that says you have
to be able to isolate the pump without effecting the FDC but I'll buy Ed's
statement since I can't refute it without actually opening a book and it
just makes sense. But lets assume a vault in the yard with a DCVA, PIV and
FDC tied in after the last control valve there, then say 200 ft of UG to a
pump with a by-pass loop and then to a manifold with five risers. Then take
the pump out completely and tell me what's different than the place next
door without a pump. In the first example do I have to run that FDC line
200' extra feet to tie it in after the pump but not do the same on the
place with no pump?

On Fri, Sep 25, 2015 at 8:22 AM, Brian Harris <[email protected]>
wrote:

> Sounds nice but I only have the 2007 edition.....
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Larry Keeping
> Sent: Friday, September 25, 2015 10:49 AM
> To: [email protected]
> Subject: RE: FDC on Fire Pump
>
> The schematic that you are remembering might be Figure A.4.20.1.2(b) of
> NFPA 20-2013, which shows a FDC downstream of all of the control valves and
> check valves associated with the fire pump installation.
>
> Larry Keeping
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian Harris
> Sent: September-25-15 9:48 AM
> To: [email protected]
> Subject: RE: FDC on Fire Pump
>
> For some reason I thought I remembered seeing a schematic but apparently
> not. So as long as the FDC ties into the pump discharge downstream of the
> discharge check valve I'm good to go correct?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Friday, September 25, 2015 9:41 AM
> To: [email protected]
> Subject: RE: FDC on Fire Pump
>
> 13 (2013) 8.17.2.4.8
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Brian Harris
> Sent: Friday, September 25, 2015 6:40 AM
> To: [email protected]
> Subject: FDC on Fire Pump
>
> Glad its Friday but I must be having a brain cramp..... Where does it
> specify where the FDC ties into the pump discharge?
>
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc.com<http://bvssystemsinc.com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to