We never make this decision. I would suggest them to put it back to the owner 
either direct or through your GC and of course document, document, document. 


Rod at Rapid

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET
Sent: Wednesday, November 04, 2015 10:10 AM
To: [email protected]
Subject: question of procedure

Say a fire sprinkler system is completed and the 200 psi test has been 
performed and passed.  The building is fully sheet rocked and very near to turn 
over.  Yet, the alarms are not in place.  Do you leave the system with the 
control valves open or closed?

Vandalism where some one opens a 2½" hose valve on the top story of a building 
can lead to a lot of water damage with no alarm to signify flow.  Arson where 
the building burns because the system was left closed since no alarms in place 
can also lead to great damage. It seems like a damned if you do and damned if 
you don't.

Is there any code/standard backing for either situation?  A customer is having 
to deal with one of these issues.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to