According to *11.2.3.4.1 *you only need to calculate 3 sprinklers in service chute when supplied by a separate riser...I am just digging for full understanding here...
If you start at the 1st floor and feed a chute through multiple floors fed from a single vertical pipe off the Dry System, does that meet the intent of a separate riser if said pipe does not have a separate control valve? If the answer is no, do you calculate it as a corridor (single row) up to 7 heads? If the vertical pipe feed a single sprinkler on each floor but they are not in a service chute and each floor is sealed from the other, can you calculate the largest room and only flow one sprinkler on the highest floor? Thanks all, Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org