I don't get to use many ring gauges - Is there any way to gauge the threads 
once the pipe is assembled to the fitting, or does it have to be tested before 
installation?

Thanks,

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph 
913.888.0618 f 
913.526.7443 cell 
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Rod DiBona
Sent: Thursday, January 14, 2016 11:46 AM
To: [email protected]
Subject: RE: Torque values?

Yes the ring gauge is the right way for the thread depth. Another issue is the 
thread quality. If the dyes weren't good or properly oiled the thread quality 
goes down and sometimes causes leaks. We had a similar case and that was the 
culprit.

Rod at Rapid

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, January 13, 2016 5:16 PM
To: [email protected]
Subject: RE: Torque values?

The proper way to determine a correct joint make up is with a ring gauge to 
test the thread depth and taper. If the threads are made properly,  then the "2 
to 3 threads showing at make-up" standard is bullet proof. If the ring gauge 
indicates the threads are deep or shallow, a "tight " joint may bottom out the 
threads or leave 4 threads showing. Both conditions can be a long term problem.
Start with ring gauges.
Mark at Aero
602 820-7894

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, January 13, 2016 5:02 PM
To: [email protected]
Subject: RE: Torque values?

Yes, the metallurgist will be doing in depth analysis of the threads, but there 
are long-standing good practices and standards for threads.   

SL

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Wednesday, January 13, 2016 4:00 PM
To: Forum
Subject: RE: Torque values?

Have you checked into the thread itself?  My old memory recalls the taper and 
threads per inch.  On 1" pipe you have 2 7/8 threads left.

AFSA course has good best practices.



Sent from my Verizon Wireless 4G LTE smartphone


-------- Original message --------
From: Steve Leyton <[email protected]>
Date: 01/13/2016 4:54 PM (GMT-07:00)
To: [email protected]
Subject: Torque values?

I have an interesting and challenging situation:

My firm is overseeing remediation of rampant leaks on all floors of the 
sprinkler systems in a 6-story building.  Our first suspect was a really bad 
MIC infection, but that's not it.  What we think we have is situation where the 
threads were not cut correctly or where arm-over and drop piping wasn't 
correctly made into the T.I. ready shell system branch outlets.   The owner has 
hired a metallurgist to do all sorts of analysis on the piping and one of the 
things we want to do is torque test some of the samples to determine whether 
they're made in correctly.   But we need a benchmark:   I know that there are 
different training methods for piping installation and that making pipe in 4 or 
5 turns by hand and then a certain number of turns by wrench is one of the 
metrics that has been widely used over the last few years.   But we have not 
been able to ascertain whether or not there's ever been a torque load value 
established for making in threads.  Can anyone help me find publishe
 d standards of care and practice for threaded piping make-ups in terms of 
torque or turns?

Thanks in advance,
Steve Leyton
Protection Design & Consulting
San Diego, CA



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to