The ones I have done with individual garages have been 13R systems. I would
assume for a 13 system, you would need one underneath since, as you say, there is no exception. Because they could be fairly low, you might want to install a
cage.

Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Thu, Jan 14, 2016 at 5:14 PM, [email protected]
<[email protected]> wrote:
NFPA 13. R doesn't require.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/14/2016 3:13 PM, Todd Williams wrote:
> 13 or 13R system?
>
> Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
> 860-535-2080 (ofc) 860-608-4559 (cell)
> Sent using CloudMagic
> [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
> On Thu, Jan 14, 2016 at 3:22 PM, [email protected]
> <[email protected]> wrote:
> Was having a discussion with a contractor the other day. Do you guys
> design/install sidewall sprinklers for under garage doors in apartment
> buildings. I am referring to the garages where it is accessible only by
> a single tenant, not a large parking garage with an apartment complex.
> I don't find anything in 13 that allows it to be eliminated. However,
> we run into a lot of these where the sidewall is not installed. Just
> curious how others approach this.
>
> --
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to