I have had the same request as an AHJ. We allowed them to pipe the system - no heads and no riser. Plans were submitted to review future head placement and to verify hydraulic calculations. We stated they were responsible for any changes to the code when water did become available. It allowed them to get the bulk mains and cross mains in the ceiling with the other mechanical systems during construction. To my knowledge they still have not put in the system (heads and riser).
DUANE T. FOX, JR., CFPS, CFI, CFPE ASST CHIEF, TECHNICAL SERVICES DE STATE FIRE MARSHAL'S OFFICE 302-856-5298 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Karen Lesko Sent: Monday, April 11, 2016 11:18 AM To: [email protected] Subject: Re: Unconnected sprinklers The Life Safety Code does say "Existing life safety features obvious to the public, if not required by the Code, shall be either maintained or removed. Karen Lesko Sent using CloudMagic Email [https://cloudmagic.com/k/d/mailapp?ct=pa&cv=8.3.8&pv=5.1.1&source=email_footer_2] On Mon, Apr 11, 2016 at 7:02 AM, Frans Stoop < [email protected] [[email protected]] > wrote: Gentlemen, Is it written anywhere in the NFPA codes or FM datasheets that it is not allowed to install sprinklers without connection to a water supply? A company wants sprinklers installed in the course of a building renovation. The sprinkler system will not be connected to a water supply yet. Sometime in the future, within a few a few years, this might change and a connection to the watersupply might be installed. We recommend to replace all visible sprinklers by hexagon plugs for the time being, to avoid a false suggestion of safety. Now the question is raised if it is written in the NFPA or FM that unconnected sprinklers are not allowed. Unfortunately, I can't find it. Another suggestion was to put a sign on the door to each room saying "Sprinklers not functional". Met vriendelijke groet/Kind regards, Frans Stoop Riskonet B.V. Singel 540, 1017AZ, Amsterdam T +31 6542 37 642 www.riskonet.com [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org