I have had the same request as an AHJ.  We allowed them to pipe the system - no 
heads and no riser.  Plans were submitted to review future head placement and 
to verify hydraulic calculations.  We stated they were responsible for any 
changes to the code when water did become available.  It allowed them to get 
the bulk mains and cross mains in the ceiling with the other mechanical systems 
during construction.  To my knowledge they still have not put in the system 
(heads and riser).


DUANE T. FOX, JR., CFPS, CFI, CFPE
ASST CHIEF, TECHNICAL SERVICES
DE STATE FIRE MARSHAL'S OFFICE
302-856-5298




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Karen Lesko
Sent: Monday, April 11, 2016 11:18 AM
To: [email protected]
Subject: Re: Unconnected sprinklers

The Life Safety Code does say "Existing life safety features obvious to the 
public, if not required by the Code, shall be either maintained or removed.

Karen Lesko


Sent using CloudMagic Email
[https://cloudmagic.com/k/d/mailapp?ct=pa&cv=8.3.8&pv=5.1.1&source=email_footer_2]
On Mon, Apr 11, 2016 at 7:02 AM, Frans Stoop < [email protected] [[email protected]] > 
wrote:
Gentlemen,

Is it written anywhere in the NFPA codes or FM datasheets that it is not 
allowed to install sprinklers without connection to a water supply?
A company wants sprinklers installed in the course of a building renovation.
The sprinkler system will not be connected to a water supply yet.
Sometime in the future, within a few a few years, this might change and a 
connection to the watersupply might be installed.

We recommend to replace all visible sprinklers by hexagon plugs for the time 
being, to avoid a false suggestion of safety.
Now the question is raised if it is written in the NFPA or FM that unconnected 
sprinklers are not allowed.
Unfortunately, I can't find it.
Another suggestion was to put a sign on the door to each room saying 
"Sprinklers not functional".

Met vriendelijke groet/Kind regards,

Frans Stoop
Riskonet B.V.
Singel 540, 1017AZ, Amsterdam
T +31 6542 37 642
www.riskonet.com
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to