When you open an FDV, water comes out, it's automatic.  Manual standpipes,
like in unheated parking garages with no water supply, just an FDC, are
manual.
Pump isn't undersized, assuming it serves HMD sprinkler requirements with
hose stream allowances, just doesn't supply standpipe demand, FDC does.
TD

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of very Cool
Sent: Thursday, April 28, 2016 8:40 AM
To: [email protected]
Subject: RE: standpipe and sprinkler pressures

Tom: That's a good point, even if the sprinkler booster pump is undersized
for standpipe requirement, and only manual wet standpipe is required, would
the standpipe be considered automatic wet in this case?
For example, if the sprinkler booster pump is 500 GPM @ 70 PSI, and
standpipe requires 1000 gpm @ 150 PSI in a combined system, would the
standpipe be considered automatic in this case, or will the sprinkler
booster pump need to become a fire pump with more flow and pressure to
achieve 100% automatic operation?