Nope, won't work and just bad practice.

I ran a quick calc, flowing as an example, 900 gpm through a 2" black carbon 
steel pipe at 109 fps, the pressure drop was 6.4 psi/ft of run.  How are you 
going to overcome the excessive pressure drop or are talking about a real small 
section of pipe where this would occur?