I apologize if this has been discussed already as I tried searching the 
archives.  All my hits were either not high piled storage, mix of high piled 
storage vs other storage arrangements with a level ceiling, or two different 
distinct roof heights.  None of these match my scenario.  So here we go....

For quick reference:

NFPA 13 (2013) - 12.3 Adjacent Hazards or Design Methods.  For buildings with 
two or more adjacent hazards or design methods, the following shall apply:

1)      Where areas are not physically separated by a barrier or partition 
capable of delaying heat from a fire in one area from fusing sprinklers in the 
adjacent area, the required sprinkler protection for the more demanding design 
basis shall extend 15ft beyond its perimeter.

2)      The requirements of 12.3(1) shall not apply where the areas are 
separated by a barrier partition that is capable of preventing heat from a fire 
in one area from fusing sprinklers in the adjacent area.

3)      The requirements of 12.3(1) shall not apply to the extension of more 
demanding criteria from an upper ceiling level to beneath a lower ceiling level 
where the difference in height between the ceiling levels is at least 2ft.

What is your opinion on this rule when you have a warehouse that is 45ft tall, 
roof slope is ¼ in 12, rack storage of class IV commodity (no solid shelves or 
open top containers), ESFR protection, at the 40ft roof elevation you change 
k-factors, so below 40ft the system is designed for K17@52psi for 35ft storage 
height @ 40ft roof, and above 40ft the system is designed for K22@40psi for 
40ft storage height @ 45ft roof.  There is no floor to roof barrier between 
areas.

Do you think the K22 design can stop at the 40ft roof height?  Or, should the 
K22 design be extended 15ft further into the area where the roof height is 40ft 
or less?

I have heard both sides of the argument.

·         No 15ft extension.  It is the same hazard "high piled storage".  The 
k-factor change is okay right at 40ft.

·         15ft foot extension should be applied.  Going to a higher storage 
height and higher roof height requires different design parameters that are 
more stringent than the lower roof and storage height, so the higher design 
requirements should be carried over.

·         Both sides agree to keep K-factors on different sprinkler systems so 
you don't overflow either system respectively.

Let me know your thoughts.

Thanks,
Sean VG