Hi Steven,

I don’t believe NFPA 13, 2007 will allow this.  In the commentary section it 
says the following concerning DIPA’s:

“The restriction stipulated in 7.2.3.10 does not apply to a preaction system, 
unless it is of the double interlock type. These types of preaction systems 
maintain air pressures typical of those of dry pipe systems and should be 
treated as such. The use of a looped piping arrangement is not prohibited for a 
dry pipe system, because the associated water delivery time delays are not as 
severe as for a gridded system.”

Best regards,

   Mike Stossel
   NICET Level IV
   Automatic Sprinkler System Layout
   1070 38th Street
   Brooklyn N.Y. 11219
   Office: 718-633-3036 ext 114
   Fax:      718-633-4593
   [email protected]<mailto:[email protected]>
  www.safetyfiresprinkler.com<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Mackinnon
Sent: Wednesday, June 08, 2016 1:44 PM
To: [email protected]
Subject: gridded pipe in a DIPA system

Just came across a set of fire sprinkler plans for a freezer… The engineer 
wants to install a DIPA with gridded pipe, would this arrangement be allowed by 
NFPA 13, 2007 standards?? I know the good book says a DIPA system is considered 
a dry system for the 30% design area increase, but what about “gridding of 
pipe”? A DIPA system would only have supervisor air… wouldn’t this help the 
water reach the open sprinkler heads similar to a wet system?

Thank you
Steven