Could they make the soffit 12in and then you could apply NFPA 13R (10ed) 6.4.6.3.2?
*From:* Sprinklerforum [mailto: [email protected]] *On Behalf Of *Jerry Van Kolken *Sent:* Thursday, June 09, 2016 2:15 PM *To:* [email protected] *Subject:* Soffits and Resid. Sprinklers I have a 1ā2ā deep soffit with a 12ā cabinet underneath. Iām protecting the room with a residential horizontal sidewall in the soffit. How would you proceed? Jerry Van Kolken *Millennium Fire Protection Corp.* 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730