Hello Ed,

That is after about the 2 min it takes the riser to trip.

Thursday, June 16, 2016, 2:43:03 PM, you wrote:

> "Get solid flow after about 2 min and for about 45 seconds to 1.5 min then it 
> goes to sputtering and then you get solid waterflow."
> Does this conflict with your initial statement?  " Water delivery is 4-5 
> minutes to the inspectors test."



> Possibly there is some water trapped in the piping in the building in which 
> the ITV is located. 


> I wonder too if the vane in the WFI might have blown off and is resting 
> somewhere downstream.




> Ed



>  
>  
>  
>  --
>  Best regards,
>   Charles                            mailto:[email protected]
>  
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  







-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to