I am not smart enough to know if an existing system will hydraulically work
when adding substantial friction loss for flex drops. I disagree with the
contention that you can change hard pipe to flexible drops without some
kind of evaluation.  This prevents us from using them sometimes but I would
rather err on the side of caution.


Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Tue, Aug 30, 2016 at 11:47 AM, <[email protected]> wrote:

> Travis,
>
>
>
> What you say here is true.  It is also very helpful as you mention when
> you have multiple areas to calculate and you can’t “eyeball” the most
> hydraulically remote.  However it isn’t without risk.  Many times we have
> done this, and during our QC process realized some of the sprinklers were
> not setup properly for the hazard they are protecting, or found that a
> sprinkler was disconnected, or accidentally picked up sprinklers we didn’t
> intend to.  Same can be said about the piping network.  Or someone
> accidentally copied a pipe that they manually overwrote 90’s Tee’s Valve’s
> etc into a straight run rather than drawing them.
>
>
>
> So, I agree AutoSprink can be very helpful with multiple calcs.  I just
> offer the word of warning to those who think computers will be replacing
> smart designers anytime soon.
>
>
>
> Thanks,
>
> Sean VG
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Travis Mack, SET
> *Sent:* Tuesday, August 30, 2016 9:14 AM
> *To:* [email protected]
> *Subject:* Re: Flexheads in small renovation (Calculation Software)
>
>
>
> And that is the beauty of software like AutoSprink.  Just put the boundary
> on the plan.  Select all of them you have and tell it to keep the
> hydraulically most demanding.  Simple and sweet.
>
> When it may be a challenge for the AHJ to believe the area I select, then
> I will submit multiple areas just to eliminate questions.
>
> The software packages today and power of the personal computer make this
> entire thread a mute point - provided the information is available.  If you
> have the system drawn, it is literally a matter of seconds to calculate an
> area.  It is not like those of us who learned by hand back in the day and
> it would be a long drawn out process.
>
> Travis Mack, SET
>
> MFP Design, LLC
>
> 2508 E Lodgepole Drive
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> email:[email protected]
>
>
>
> http://www.mfpdesign.com
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 8/30/2016 9:08 AM, rongreenman . wrote:
>
> I'd agree with Mark except for two little irritations of mine when
> discussing this. "Remote Area" was a term that worked when we just
> sprinklered big boxes that housed either factories or warehouses as the
> "remote area" (furthest from the rider) was typically the hydraulically
> most demanding area. These days that area can be anywhere (a grid being the
> always example). Hydraulically most demanding area is too muchoif a
> mouthful for describing itself so I just prefer design or demand area. This
> pet peeve came about from teaching newbies the basics as they'd often get
> it in their minds that remote meant furthest away and so would want to
> calculate the the x number of heads at the greatest distance as the crow
> flies over the plan. That is also the basis of pet peeve two that "remote
> area" also suggests that there is only one possibility and it's easy to
> find. Determining the design area(s) is an art. I have an exercise based on
> a building no one would ever build but it gas over a dozen potential design
> areas and just as Mark says the student needs to determine where and which
> are most likely by estimating demand at each location.
>
>
> On Tuesday, August 30, 2016, <[email protected]> wrote:
>
> My personal belief is that the designer “designs” the “remote” area into
> the system, and a good designer will design the overall system to
> economically benefit from “where” the remote area lies. Unfortunately, I
> think most systems are laid out, sized, and then calculations are performed
> to determine where the remote area lies.
>
> As Steve says “just my opinion”
>
> Mark at Aero
>
> 602 820-7894
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Bill Brooks
> *Sent:* Tuesday, August 30, 2016 8:32 AM
> *To:* [email protected]
> *Subject:* RE: Flexheads in small renovation (Calculation Software)
>
>
>
> You will be able to tell this question is based on minimum software
> application experience, but does current software automatically determine
> “most demanding”?  Or, is it up to the human operator to guess where this
> area might be?  If it’s a guess, how do you know you have chosen correctly?
>
>
>
> Bill Brooks
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Steve Leyton
> *Sent:* Tuesday, August 30, 2016 10:40 AM
> *To:* [email protected]
> *Subject:* RE: Flexheads in small renovation
>
>
>
> To underscore John’s point, these fittings impose with a SUBSTANTIAL
> pressure loss.   As 3rd party, we would ask for calculations to prove the
> performance of the revised configuration.
>
>
>
> SL
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Michael Hill
> *Sent:* Tuesday, August 30, 2016 6:11 AM
> *To:* [email protected]
> *Subject:* RE: Flexheads in small renovation
>
>
>
> I agree with Richard, it needs to be evaluated. It is known that flex
> piping is generally more demanding than their hard piped counterparts. If
> the base building design did not include flex piping, I would look at it as
> a change to base building design and perform a quick calculation to see how
> it looks. I assume they didn’t use excessively long flex pipe with more
> bends or lops than were needed.
>
>
>
> Mike Hill
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Todd Williams
> *Sent:* Tuesday, August 30, 2016 8:39 AM
> *To:* [email protected]
> *Subject:* RE: Flexheads in small renovation
>
>
>
> This is a single story building. Multiple looped 4" and 3" cross mains
> with branches to wings. (Think nursing home with interior court yards). No
> fire pump. 100 psi static with a flat curve (2 year old test, DeltaE = 0).
> Area in question not most hydraulically remote but toward that end of the
> building. Branch lines are fed from the loop, not a DE branch main. LH
> occupancy.
>
>
>
> I am not worried about this not being adequate, more a consensus of what
> needs to be done and what is correct.
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-608-4559 (cell)
>
>
>
> Sent using CloudMagic
> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>
>
>
>
> On Tue, Aug 30, 2016 at 8:22 AM, Richard Carr <[email protected]> wrote:
>
> I can’t disagree with John (Hi John) but we need more info to make the
> call,
>
> In remote area?
>
> Fire pump?
>
> What is safety margin on existing?
>
> What is friction loss on the flex?
>
>
>
> Just because you add 4 flex piping to an existing system does not require
> it to be calculated. But does need to be evaluated.
>
>
>
> Richard Carr, SET
>
> Branch Manager
>
> Cox Fire Protection, Inc
>
> 6555 Grace Lane.
>
> Jacksonville, Fl. 32205
>
> [email protected]
>
> 904-781-8227
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *John Irwin
> *Sent:* Tuesday, August 30, 2016 7:14 AM
> *To:* [email protected]
> *Subject:* RE: Flexheads in small renovation
>
>
>
> I disagree with Richard. (Hi Richard!)
>
>
>
> Relocating these sprinklers with flex heads may very well change the
> location of the most hydraulically remote area to the place you are
> working. Flex-heads come with a substantial pressure loss. Even if doing
> calculations wasn’t required, I would want to do them for myself for peace
> of mind. My belief has always been that you can’t tax the system without
> verifying that it still works.
>
>
>
> *John Irwin*
>
> Manger – Fire Sprinkler Division
>
>
> *Critical System Solutions, LLC *Cell:     813.618.2781
>
> Email:  [email protected]
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Richard Carr
> *Sent:* Tuesday, August 30, 2016 7:08 AM
> *To:* [email protected]
> *Subject:* RE: Flexheads in small renovation
>
>
>
> Are the relocates in the remote area? if not I would not calc. also , some
> flex brands are better that others as far as friction loss.
>
>
>
> Richard Carr, SET
>
> Branch Manager
>
> Cox Fire Protection, Inc
>
> 6555 Grace Lane.
>
> Jacksonville, Fl. 32205
>
> [email protected]
>
> 904-781-8227
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Todd Williams
> *Sent:* Tuesday, August 30, 2016 6:30 AM
> *To:* [email protected]
> *Subject:* Flexheads in small renovation
>
>
>
> I have a client that did a 4 sprinkler relocate job in an office and used
> Flexheads (no sprinklers added). If the sprinklers were connected with hard
> pipe, I would probably not do hydraulic calculations. Given that we have
> FHs, should I be doing a full 900 or 1500 sqft calculation?
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-608-4559 (cell)
>
>
>
> Sent using CloudMagic
> <https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2>
>
>
>
>
>
> --
> Sent from Gmail Mobile
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>