Thank you all for the feedback. The owner and contractor would like to
change the slatted ceiling plan to ACT. 

The contractor is pushing as the sprinkler issues above the ceiling go away.

 

Will what happens.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                            <mailto:tston...@comcast.net>
tston...@comcast.net

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Steve Leyton
Sent: Thursday, September 15, 2016 11:17 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Noncombustible concealed space

 

If I'm visualizing the situation correctly from your description, I think
the duct is creating a cloud condition, with a wide flat bottom surface that
has openings between the sides and the corridor walls.   Looking to the
cloud provisions in the new edition of the standard, you don't need
sprinklers above the duct and can measure deflector distance from the bottom
surface.

 



 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Tim Stone
Sent: Wednesday, September 14, 2016 7:04 PM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Noncombustible concealed space

 

I have an interesting situation. 

 

Steel and concrete School building. A Corridor runs down the middle on each
floor about 8' wide, W12 steel I-Beams forming the side at the floor deck
above, (About 12'-0 Floor to Bottom of deck).

There is a large duct running the length of the Corridor about 7'-6 wide x
24" tall. This leaves a gap of about 3" on each side between duct and
sheetrock partitions. The top of the duct is about 11" below the steel
Q-Deck above.

An open metal grid ceiling system is installed 12" - 16" below the duct. 

 

We are installing upright heads 1"-4" below the duct allowing the water to
spray down through the open grid ceiling.

 

The question is, do I need to install heads above the duct? There will be no
way to service or replace these heads and if installed between the duct and
the wall, the head will not meet the minimum 4" off the wall.

Referencing 2010 ed. 8.15.1.2.1, concealed spaces, I believe I am following
the intent.

 

Thank you in advance.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                            <mailto:tston...@comcast.net>
tston...@comcast.net

 